Just done an EICR and all tested fine, until I got to the RCD's. It's a dual RCD board, not sure if it's TNCS or TNS as it's a top floor flat fed with T&E.
The RCD's failed to test via the circuits and so I tried the test buttons and they didn't work either. Could it just be both RCD's have failed or am I missing something obvious (which in all fairness is very possible with my brain at the moment!) Could it just be because they are AC type?

TIA
 
try turning them off and back on a couple of times.
They can get "stuck" with prolonged periods of being stationary.

bottom line, if your tester is going well over 30mA and they are not tripping, then they are faulty.
test button not working is a fail on its own.
 
As Tim said,

It could be possible but not common for both RCD's to fail, unless they have been damaged somehow or stood for a long period of time, as James mentioned. Even so, I'd be suspicious of sticking RCD's and would recommend a swap out even if they prove to be unstuck and test ok.

If it turns out they are faulty then they obviously need replacing.
 
If the power is on and the fail the self-test button then I would replace them.

Whatever the reason they are not providing the safety benefit expected of them, or cannot demonstrate it when tested. Sometimes devices get stuck and a mechanical cycle or two can fix it, but unless they then pass all tests (test button and ramp, etc, using the MFT) it is still time for a replacement.
 
Disconnect the output neutral from the RCD on the main neutral connection to remove all the circuits neutrals. Leave all the breakers that the RCD feeds in the off position. Retest the RCD. If it doesn't trip now then the RCD is faulty.
as above. a N-E fault on any curcuit could cause both RCDs to fail to trip
Yes good point, I've had this situation in the past, never give it a thought in response to the OP!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
KInross
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
RCD's not tripping at all
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
Walks_23,
Last reply from
Intoelectrics,
Replies
8
Views
3,111

Advert

TrueNAS JBOD Storage Server

Back
Top