If your trip tests were done with no external loads on the circuit then they do reveal the RCD is faulty and replacing it should resolve the symptoms.
However there should not normally be leakage up to 15mA on a circuit in a house so it may be worth checking that your IR results for the protected circuit are not significantly low, it is probably a minor peak in current since it is intermittent but worth checking the circuit is not damaged.
However there should not normally be leakage up to 15mA on a circuit in a house so it may be worth checking that your IR results for the protected circuit are not significantly low, it is probably a minor peak in current since it is intermittent but worth checking the circuit is not damaged.