Hi Guys.
I went to see a job today where customer wanted to replace front plate of sockets and switches. Switches has no cpc but cpc is present in the cieling roses. As I opened consumer unit the main switch was 80A 2 pole RCOCB bs 4293 which has 100mA rated tripping current and 2000A breaking capacity. My question " Is it acceptable in dwellings". customer doesn't want to upgrade consumer unit. Please advise . Thanks in advance
ccu4.jpg
ccu2.jpg
 
If the RCD works, I'd get on with it and get out of there!
If it doesn't, this is one where you could easily open a large can of worms that I'd personally choose to keep shut. It would be a rather challenging CU change if it turns out to be required. (Inset CU and looks like conduit for CPC). It's fairly likely the 100ma RCD is for fault protection of a TT system, or maybe it was TT once and is now PME.
I'd do a Zs@DB (remembering there could be parallel paths). If inconclusive I'd test local incoming earth (disconnected) with main switch off .
If I got higher that TNS numbers back I wouldn't get involved beyond advising in writing to customer that the fault protection of their installation couldn't be confirmed and more work is needed to investigate and rectify.
 

Reply to RCOCB BS 4293 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
768
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top