Taken from Extracts
You have to put in the studying
GN-3 : P/35
Method 2 . ( R[SUP]2[/SUP] ) Testing bonding conductors & earthing conductors
re-cap ,
To confirm the continuity of these protective conductor's , test method 2 may be used .
This method can also be used to confirm a bonding connection between extraneous-conductive-part , where it is not possible to see a bonding-connection e.g.
P/34
Test method 2 ... ( for circuit )
re-cap ,
This test measures the continuity résistance of the circuit protective conductor , ( R[SUP]2[/SUP] ) which should be recorded on a , Schedule of Test Results
( see earlier note " Parallel earth parts & effects on test readings )
P/32 , 2.7.5. Continuity of protective conductors , including Main & Supplementary bonding
Regulation 411.3.1.1. requires that installations which provide protection against electric-shock using ( ADS ) must have a circuit protective conductor ( run ) to & terminated at each point in the wiring & each accessory , refer .
Regulation 612.2.1. requires that a continuity check be carried out on all circuits including ring-circuit's
There are ( Two widely used test methods ) that have evolved for checking conductor continuity , also measures ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) which , when added to the external impedance ( Ze ) enables the earth fault loop impedance ( Zs ) to be checked against the design
P/33 , Test method 1 ... ( for circuit ) Connections for testing continuity of protective-conductors
2.7.6. Continuity of ring-final-circuit-conductor(s)
Three-steps test is required to ( Verify the continuity ) Etc refer
Regulation 612.2.2.
You have to put in the studying
GN-3 : P/35
Method 2 . ( R[SUP]2[/SUP] ) Testing bonding conductors & earthing conductors
re-cap ,
To confirm the continuity of these protective conductor's , test method 2 may be used .
This method can also be used to confirm a bonding connection between extraneous-conductive-part , where it is not possible to see a bonding-connection e.g.
P/34
Test method 2 ... ( for circuit )
re-cap ,
This test measures the continuity résistance of the circuit protective conductor , ( R[SUP]2[/SUP] ) which should be recorded on a , Schedule of Test Results
( see earlier note " Parallel earth parts & effects on test readings )
P/32 , 2.7.5. Continuity of protective conductors , including Main & Supplementary bonding
Regulation 411.3.1.1. requires that installations which provide protection against electric-shock using ( ADS ) must have a circuit protective conductor ( run ) to & terminated at each point in the wiring & each accessory , refer .
Regulation 612.2.1. requires that a continuity check be carried out on all circuits including ring-circuit's
There are ( Two widely used test methods ) that have evolved for checking conductor continuity , also measures ( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) which , when added to the external impedance ( Ze ) enables the earth fault loop impedance ( Zs ) to be checked against the design
P/33 , Test method 1 ... ( for circuit ) Connections for testing continuity of protective-conductors
2.7.6. Continuity of ring-final-circuit-conductor(s)
Three-steps test is required to ( Verify the continuity ) Etc refer
Regulation 612.2.2.