For Amberleaf:
BS-7671:2008: Requirements for electrical installation(s) ... 542.4.
Main Earthing Terminal
MET)
Disconnection of ..........
1 ) Means for disconnecting the earthing conductor
Regulation 542.4.2 of BS-7671 requires means for disconnection of the earthing conductor be provided at or near the Main Earthing Terminal (MET) of an installation. The purpose of the means of disconnection is to allow measurement of the external earth fault loop impedance ( Ze ) and, where the installation forms part of a TT system , measurement of the installation earth electrode résistance.
Regulation 542.4.2 is reproduced as follows for ease of reference
Regulation 542.4.2
‘ To facilitate measurement of the resistance of the earthing arrangements, means shall be provided in an accessible position for disconnecting the earthing conductor. Such means may conveniently be combined with the main earthing terminal or bar. Any joint shall be capable of disconnection only by means of a tool. ‘
As Regulation 542.4.2 does not stipulate a particular arrangement for the means of disconnection, any suitable arrangement may be used which meets all the requirements stated in the regulation. Examples of suitable arrangements are given in Figures
1 and
2.
Fig 1, shows an arrangement in which the earthing conductor is withdrawn from its terminal at the MET, by the use of a tool (a screwdriver), in order to facilitate the resistance measurement of the means of earthing, and then replaced and re-secured into the terminal after the measurement has been made. This arrangement is
not suitable for situations where the end of the earthing conductor at the MET cannot be conveniently manoeuvred, such as within an enclosure in which there is insufficient room or where the diameter of the earthing conductor is too large to provide sufficient flexibility.
Fig 2 , shows an example of a MET incorporating a bolted link which is opened or removed by the use of a tool ( such as a spanner ) in order to disconnect the earthing conductor, and then reinstated and re-secured after the resistance measurement to the means of earthing has been carried out.
Whatever arrangement is provided as the means for disconnection of the earthing conductor, in addition to the requirements of Regulation 542.4.2 mentioned earlier, the requirements of the Electricity at Work Regulations and those of Section 522 of BS-7671 must be met.
Regulation 9 of the Electricity at Work Regulations requires that ‘ if a circuit conductor is connected to earth or to any other reference point, nothing which might reasonably be expected to give rise to danger by breaking the electrical continuity or introducing high impedance shall be placed in that conductor unless suitable precautions are taken to prevent that danger ’.
For example, where a joint or bolted link is provided, it must be arranged to ensure the integrity of the conductor. The connection or link must not be able to be removed in such a way as would give rise to danger. Ways of achieving this would normally include one or more of the following:
• Disconnection requires a deliberate act using a tool
.... This is an
explicit requirement of Regulation 542.4.2
• The joint or link should be accessible only when the installation is isolated
• The joint or link should be accessible to skilled persons only
• Section 522 of BS-7671 requires that the means for disconnection must be protected where necessary against external influences (such as vandalism, unauthorized interference, damp, corrosion, dust, vibration or mechanical impact).
Earthing conductor at the MET. Earthing conductor is withdrawn from its terminal for testing purposes. Withdrawal is a deliberate act involving the use of a tool.
Example of MET with disconnectable link
Testing : ( MET )
542.4.2. To facilitate
measurement of the résistance of the earthing arrangements ,
Mean'
s ; shall be provided in an accessible position for disconnecting the (
Earthing-
conductor ) Such means may conveniently be combined with the
main-
earthing-
terminal or bar .
Any joint shall be capable of disconnection only by
means of a tool .
Main Earthing Terminal : (MET)
1.
The requirement to have a Main Earthing Terminal (MET)
Regulation 542.4.1 of BS-7671 requires a Main Earthing Terminal (MET) be provided for every installation.
The MET is required to connect the following to the earthing conductor of the installation, as illustrated in Fig 1 (Regulation 542.4.1 refers):
i) The circuit protective conductors
ii) The protective bonding conductors
iii) Functional earthing conductors (if required)
iv) Lightning protection system bonding conductor, if any (see Regulation 411.3.1.2).
MET connecting various conductors to the earthing conductor, as required by Regulation 542.4.1.
For practical reasons, the MET is normally situated at or near the origin of the installation (that is, the position where the electrical energy is delivered)
(
Means of earthing) ....................... TN- TT systems
Example of the use of the earthing bar as a MET in an item of main switchgear
R/P 26
Distribution board :
An assembly containing switching or protective devices ( e.g. fuses , circuit-breakers , residual current operated devices ) associated with one or more outgoing circuits fed from one or more incoming circuits , together with terminals for the neutral and circuit-protective-conductors . refer
R/P 25
Consumer unit : .. ( CCU )
may also be known as a consumer control unit or electricity control unit . refer
Examples of brass terminal bars or blocks used as a MET
MET incorporating a bolted link to permit the disconnection of the earthing conductor for testing purposes