Voltage drop using tables from BS-7671:2011:
Example:
Circuit is wired using 70°C thermoplastic flat T&E cable
- Copper 2.5mm[SUP]2[/SUP] live-conductor(s) & 1.5mm[SUP]2[/SUP] circuit-protective-conductor
- Circuit is 30 metres long
- Carry a current of 17 amperes .. supply voltage 230V
( Vd ) for this cable can be find using :
:icon_bs: Table 4D5 Appendix 4 of BS-7671:2011: P/340
2011: O.S.G. Table F6 . P/150
Using either of ( Table 4D5 or O.S.G. )
4D5 ) The voltage drop for 2.5mm[SUP]2[/SUP] copper cable is ( 8 ) → 18mV/A/m
O.S.G. ) The voltage drop for 2.5mm[SUP]2[/SUP] copper cable is ( 8 ) → 18mV/A/m
18mV/A/m millivolts x amperes x distant in metres ( as value is in millivolts it must be divided by 1000 to convert to Volts )
Circuit is by calculation : 18mV x 17A x 30m Ă· 1000 = 9.18
Point to note : This volt drop value used in BS-7671: has been rounded up for ease of calculation .
Example:
Circuit is wired using 70°C thermoplastic flat T&E cable
- Copper 2.5mm[SUP]2[/SUP] live-conductor(s) & 1.5mm[SUP]2[/SUP] circuit-protective-conductor
- Circuit is 30 metres long
- Carry a current of 17 amperes .. supply voltage 230V
( Vd ) for this cable can be find using :
:icon_bs: Table 4D5 Appendix 4 of BS-7671:2011: P/340
2011: O.S.G. Table F6 . P/150
Using either of ( Table 4D5 or O.S.G. )
4D5 ) The voltage drop for 2.5mm[SUP]2[/SUP] copper cable is ( 8 ) → 18mV/A/m
O.S.G. ) The voltage drop for 2.5mm[SUP]2[/SUP] copper cable is ( 8 ) → 18mV/A/m
18mV/A/m millivolts x amperes x distant in metres ( as value is in millivolts it must be divided by 1000 to convert to Volts )
Circuit is by calculation : 18mV x 17A x 30m Ă· 1000 = 9.18
Point to note : This volt drop value used in BS-7671: has been rounded up for ease of calculation .