RCDs are used to provide protection
• fault protection
• additional protection
• protection against fire
An RCD is a protective device used to automatically disconnect the electrical supply when an imbalance is detected between live-conductors.
In the case of a single-phase circuit, the device monitors the difference in currents between the line and neutral conductors.
The term ‘ live ’ conductor includes both the line & neutral conductors .. residual current
Additional protection - RCD test (5 x ) 500% fast test
Fault current IΔn .. Sensitivity - instantaneous only (A) 0.03A
RCD .. In) rated current of the contacts, expressed in amperes . e.g.
The testing device then allows a larger fault current (normally 150mA) to flow. This should trip the RCD more quickly, again within a predetermined time for the type of RCD and supply.
An RCD does not provide protection against Overcurrent
Overcurrent protection is provided by a circuit breaker
Residual current operated circuit-breaker (RCBO) with integral overcurrent protection
O.S.G.
• Overload
• Short circuit
• Earth fault
Manufacture details & information.
Residual current operated circuit breaker with Integral Overcurrent Protection ( RCBO)
A residual current operated circuit-breaker designed to perform the functions of protection against :
(Iƒ) fault current
• Short circuit
• Earth fault
• Overload
These devices comply with BS-EN-61009-1
Technology : There are two-types of residual current devices
• Electromagnetic .
• Electronic .
- Electronic devices do not need such a sensitive torroid as electronic circuits within the device amplify the signal to operate the trip relay .
However, these devices often require a safety earth reference lead to ensure that the device will continue to operate in the event of the supply neutral being lost , The power to trip the device is taken from both the fault-current and the mains supply .
(RCBOs) These devices should be disconnected whilst carrying out Insulation résistance to prevent damage to the device and to avoid incorrect test results .
Regulations RCDs
States : The test results should be within the parameters set out in Table 3A .. “ performance criteria ”
Standards’
Only - BS-4293 had a limit of 200mS .. 1983 (1993) replaced by: still out there
(G) BS-EN-61008-1 ( RCCB )
(G) BS-EN-61009-1 (RCBO)
5 x IΔn (500%)
when periodically testing a RCD , it is often advisable to undertake the 5 x IΔn test first .
if the device fails this test , it is a good indication that the quarterly test button check has not been carried out and ? dirt or dust on the contacts may be causing a slower operation than normal or ( just seized up )
Before you reject the RCD , completely, the test should be carried out twice more, as it is quite usual for the device to operate properly after these two-subsequent operations