Well I must say that Northstar and me work well together, good little team up today mate, I enjoyed it. You were thrown in at the deep end but worked most of it out yourself, impressed. Not a straight forward job, few things to think about. Here are the findings, lets see what you would do???
TN-C-S, 100A main fuse, no Isolation switch, 25mm tails less than 3m at present.
10mm main Earth to the incoming MET at the incomer head.
Gas bonding in 10mm going straight to the incomer head.
Water banding 10mm going to the BS3036 MET C/U. (old re-wire-able btw)
Old C/U is loose and moves when you pull a fuse out!
C1= Full house sockets. 3 x 2.5mm in one 30A fuse?
C2= 7.5Kw shower in 6mm on a 30A.
C3= Immersion heater in 4mm on a 20A.
C4= Full house lights 1.5 on a 5A.
Now the difficult bit, the customer!!!!
He wants the C/U moving from under the sink cupboard to the one above. Most cables are coming from above so only the Tails, water bonding and the 2.5mm "socket cables" need to be extended.
Q. How do we achieve this?
We have 3 x 2.5mm for the sockets in one 30A MCB atm! Because of the house being full of kids, parents, grand parents and they do not have the time today for us to be there for long, unable to test and confirm if it is 3 x radial circuits, 1 x RFC + 1 x radial??? This will have to be confirmed at the C/U change point. I personally think and Northstar agrees, after looking at this house it will be 1 x RFC for the full house and the extra cable is a spur from the CU to one or more points in the kitchen. We saw that extra sockets and a Switched fused spur have been added in the past 10-15 years. This will be addressed once we start testing when we change the CU. Not ideal but it is what we have to play with.