...now I installed my first earth rod on saturday! I was expecting a really high Ze as up to 200ohms is allowed by BS7671. My Ze was 0.34. Does this seem odd to anyone that has done one/many before?
 
It's unlikely you'll get that from one rod Luke, possible but unlikely. As the other lads have said, are you sure you were testing properly IE only using the main earth cable?
 
As alluded, I'd expect 200 - 10 Ohms, not 0.34. I would suspect there is a parallel path (Main Water Service Bond) and ....the water pipe is connected to next doors, who are TN.

?

Seen it a few times.

In fact seen an install that appears that the spark that installed it decided that it WAS a TN system (its not its TT)- No RCDs. Naughty.
 
.....I installed my first earth rod on saturday......My Ze was 0.34

This is the stuff dreams are made of, I can only wish one day this might happen for me :(

Anything is possible but that reading from a single rod with no parallel paths is a long shot. Are you sure about the test equipment and proceedures you used?
 
it was a 5/8" rod. Just one. Don't think there would have been any parallel paths as the water bond was not connected as the water pipe isn't installed yet.

The CU I installed was fed from a 3 phase fuse board at one end of some stables. A 4mm armoured cable supplied the new CU. The original 3 phase board had a Ze of 0.25 (don't know if this is relevant) The original 3 phase board is supplied in armoured cable and is earthed by the metal armouring back to the suppliers facility. I have earthed the 4mm armoured at the supply end, and used the earth rod as the earth for the new consumer unit as it will have a water supply installed.

Please, any advice will be appreciated as I am a domestic electrician and very VERY rarely deal with anything else.
 
Luke, sounds like happy days mate but if I were you I'd check it again just to make absolutely sure. Go through it step by step with GN3 in your hand just to be on the safe side.
Let us know the outcome please
 
I will be going back in a few weeks to start some other work so I will double check then. Would it hurt to use the armouring of the 4mm as a sort of back up earth? And again please be gentle if this is a stupid question.

Thanks for your responses!
 

Reply to Really low Ze from earth rod! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
818

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
999

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top