Really low Ze from earth rod!

L

LukeBuckaz

Please be gentle...

...now I installed my first earth rod on saturday! I was expecting a really high Ze as up to 200ohms is allowed by BS7671. My Ze was 0.34. Does this seem odd to anyone that has done one/many before?
 
Just the difference between 3/8" rod and 5/8" rod is a lot though isn't it, I can't believe how many people just stick in 3/8" rod, I have only used these for temporary stakes for genny's and cabins.
Hell yeah mate I won't use those little bloody twigs, I've seen them used a million times and then heard"Oh that'll be fine".
Not in my book
 
the CU is metal clad but the earth from the armouring or that 3rd core was not connected. I will go back, disconnect the earth rod conductor from the earth bar and re-test. Would it hurt to connect that 3rd core of the armoured into the earth bar?
 
You need to disconnect all parallel paths dude, the only way to effectively do that is to disconnect from MET and test to that only, I think you may have been reading through the SWA.

Did you get my personal message?
 
yes the armouring is earthed but it is glanded to a seperate metal clad box, not the metal clad fuse board. Sorry I didnt make this clear.
 
When I go back I shall definitely disconnect from the earth bar and retest. If the reading was through a parallel path, and the reading through JUST the earthrod was unacceptable, I shall obviously install more earth rods until an acceptable reading is obtained!
 
yes the armouring is earthed but it is glanded to a seperate metal clad box, not the metal clad fuse board. Sorry I didnt make this clear.

Is there any chance that you've screwed these metal enclosers through plasterboard (or what ever) and into cellotex or other foil insulation which could give you a path between the two?
 
I very much doubt there are no parallel paths. But i am taking on board trev's & others post's as i usually use the twigs, I will start using the 5/8 and try and get a couple in. I hate putting rods in just in case you hit any service pipes.

Cheers
 
I personally can't see how a single 1m rod of any size can give a value that low... To measure your Ra value, the rods earthing conductor is tested in isolation to any other earthing conductors, bonding conductors or CPC's...

Maybe a rod driven into ground that's been soaked with effluent for many years (such as on a farm) may give a lower value, but then the electrode isn't going to last too long at all, unless it's made of a high grade Stainless Steel... lol!!

I wonder how many electricians just lately have been thinking that they've done well with values they have obtained, mainly due to driving a rod into water sodden soil?? Perhaps they all ought to go back and check again after a dry period!! The truth is, if they have only driven in a single rod, the chances are that the TT system they were so proud of, has risen in value by many ten's of Ohms and in all probably is'nt even stable....
 
Vic will look special once the upgrade is complete!!! Westfield, the owners, usually do a quality job! Some of their big centres in Oz are quality and they did a sterling job of the old Eagle centre in Derby! Broadmarsh needs rebuilding! Currently in Lace Market which I don't mind, but right next to some god awful flats filled with all sorts!!!
 