I have a 3 phase cooker range to install on unbalanced loads 47a / 9a / 9a.
Apparently.... I need to confirm that..
it needs a new supply that is rcd protected.
My problem is the board that it is coming from is a old memshield board 3 phase with all individual bs88 fuse carriers and no main switch isolator.
ive not come across one of these before. Usually it's a new mcb in the board and job done.
looking on the fuse carriers they mostly say 30a which I'm thinking I can't put a 50a fuse in them so would I need a new carrier?
my original idea was to put an ad box mounted to the side of the board and bring tails from the 3 phases neutral and earth through to a 3 phase rcd/mcb set up.

50a bs88 fuses - rcd - mcb - rotary isolator - appliance

i have pictures of the board and fuse carrier but don't know how to put the pics on here..?

any help or guidance would be appreciated.

thanks
 
not all three phase appliances are balanced loads. you cant just say oh 63a total that means 21a per phase.
if you got 8 elements 2 running at different wattages to the other 6 split over 3 phases it wont work out equal.

How much work have you done with 3 phase loads? I'm guessing not a lot! If a 3ph appliance is quoted as requiring a 32A supply for example it needs a 32A 3 ph supply. NOT a total of 32A if you add all the phases up.

No an appliance won't always be balanced but the manufacturer will have taken this in to account when writing the spec for the supply it needs.

Spec'ing a 3ph supply by how many amps each phase needs is in the least a very daft idea!
 
i dont even know why this thread exists.

in 3 steps

1. check appliance for brand
2. check for model on sticker/unit
3. go on there website or call them and they will tell you what is the minimum supply it needs.

why is this so difficult it takes minutes
 
i dont even know why this thread exists.

in 3 steps

1. check appliance for brand
2. check for model on sticker/unit
3. go on there website or call them and they will tell you what is the minimum supply it needs.

why is this so difficult it takes minutes

IN ONE STEP!

Get a qualified electrician to do the work!

How many times?!
 
How much work have you done with 3 phase loads? I'm guessing not a lot! If a 3ph appliance is quoted as requiring a 32A supply for example it needs a 32A 3 ph supply. NOT a total of 32A if you add all the phases up.

No an appliance won't always be balanced but the manufacturer will have taken this in to account when writing the spec for the supply it needs.

Spec'ing a 3ph supply by how many amps each phase needs is in the least a very daft idea!


we've established its 3 phase and also established its total load is 63a.. where did i say it needs to be on a 63a supply because thats what all the phases add up to?
i didnt, i said ive been given this load information which doest look quite right but ill find out monday, but just because it is total load is 63a does not necessarily mean its 21a per phase which some people didnt get but #32 clarified what i was trying to get across.
there will be a data plate on the back which will explain all and also prove the info i got given isnt quite right. so until then its irrelevant, i needed to know about the board mainly which i wasnt familiar with which i got on #26.
the rest i can deal with when i get there..
thanks for the answers, its been amusing.
D Skelton no hard feelings, its all banter. but if you not going to answer any questions then its a waste of time typing.
 
we've established its 3 phase and also established its total load is 63a.. where did i say it needs to be on a 63a supply because thats what all the phases add up to?
i didnt, i said ive been given this load information which doest look quite right but ill find out monday, but just because it is total load is 63a does not necessarily mean its 21a per phase which some people didnt get but #32 clarified what i was trying to get across.
there will be a data plate on the back which will explain all and also prove the info i got given isnt quite right. so until then its irrelevant, i needed to know about the board mainly which i wasnt familiar with which i got on #26.
the rest i can deal with when i get there..
thanks for the answers, its been amusing.
D Skelton no hard feelings, its all banter. but if you not going to answer any questions then its a waste of time typing.

Definitely speak to the manufacturer on this one. There is also load diversity that you can apply to this. See what they suggest for the supply. Once you have ascertained this, take existing phase loadings into account when connecting your unbalanced load to balance it out the best you can.
 

Reply to Really old memshield 3 phase board. New install. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
376
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
698

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top