Client decided they couldn't wait a few weeks for me to do an EICR so got someone 'off the internet' who immediately failed it (probably fairly, since its a house, with fuse wire protection on all circuits it appears).
Looking at the report for a second opinion and under operational limitations is:
"only live testing done due to fish tank not being allowed to being turned off" (sic)
and they carried out Zs only on all circuits (no idea if the fish tank also has lighting, boiler and cooker connections!)
Also didn't take rfc resistances for 2 different socket circuits, when I assume the fish tank is only connected to one....
Obviously this happens on commercial EICRs quite often where machines have to be left on, but is this a reasonable limitation on domestic cases? I'd say it's at least not in the spirit of the idea of EICRs as they are meant to be used for the domestic rental sector.
The report is probably reasonable otherwise, with a couple of arguable C2s but some clear ones too..
£710 quote for new CU and bathroom lights is not the worst rip off I've seen either - if a bit overkill since they've also done the report. (though depends if that is RCBO all circuits or Screwfix special)
I wouldn't consider a 'live testing only' certificate to be a reasonable test of a domestic electrical installation, but maybe others do?
post it, love seeing other carp paper work .
I've seen a lot worse to be fair - though always more fun to critic other paperwork than double check my own...
Not sure why the LIM for Ze though - not like they even did Zs at the board...
Bet the bathroom downlights are actually over 2.25m anyway, or not more than a C3 anyway
I'll go and take a look to ensure they haven't completely misread what's there - and then quote well under £710 for a consumer unit change which should solve any problems.
And since there are two socket circuits, they could surely have rigged something up to test both -
I'll have to try to rig something up for the poor fish when changing CU I guess ????
page1.jpg Page2.jpeg Page3.jpeg Page4.jpg page5.jpegPage6.jpeg page7.jpegpage8.jpeg
To be fair if client doesn’t want electric turned off. Then the inspector is stuck.
I did an EICR one and couldn’t turn of one of the consumer units to do dead testing because owner didn’t want his recording studio without power as he was doin* recordings.
this is dispite me telling him prior to arrival all power would be turned off .
what else can you do.
Most landlords seem surprised when I say I'll be there for 3-4 hours and that power will be off and on intermittently - I guess they are only used to the gas one which takes less time (but happens more often)
I would agree I've seen worse reports.
Just a few comments:
I'm going to assume if it's a Wylex 3036 board that the cover cannot be removed if the fuses are in place. Hence the limitations on Ze and PFC.
Nominal voltage U should be not applicable, not 240 volts.
The extent says 100% testing and 25% visual inspection. How can it be 100% testing if no dead tests or Ze test are done? And how can accessories be inspected with the power still on?
How has insulation resistance testing been done with the power on? Results show >200 M ohms for every circuit.
Why is supplementary bonding not applicable, instead of being a C2 as there are no RCDs?
I'm sure others will find more.
I'll bet the price was the same as a full test.
Absolutely agree. Some people are amazed that you have to turn the power off at all to do an electrical job. Even just the circuit your working on.
one customer who wanted an extra socket didn’t want the sockets turned off as he would loose his internet connection. He said I should have warned him. !!
another customer asked if I could wait until her bread was finished in her bread making machine.
countless customers start there washing before I get to them or even just after I have arrived.
barmy
Good point on the reason for no Ze - that is likely why - hadn't considered that, though I doubt the fish would have asphyxiated if everything had been off for 1 minute to take the lid off.
The Nominal voltage and IR tests will be poor form checking - they are the defaults on Easycert - the nominal voltage was picked up by an NICEIC bod a few years back on one of my certificates so I'm careful to remove it now. >200 is the default setting if you don't change it I believe too..
I did notice the supp bonding inconsistency - it might just be there and not looked/tested for - (or possibly no extraneous parts), and that would resolve the C2 with RCD on bathroom lights - but I think a new CU is needed regardless...
I know fish need their "life support" of heater (if tropical) and cleaning pump/filter, but from my memory of having fish as a child (as pets, not food sort) a tank can go for an hour or more with no real effects as it takes some time for the temperature to change by a serious amount.
Also what is the plan for a power cut?
Went to take a look at this job for a second opinion.
Report was accurate as far as it went - Wylex with plug in MCBs - house with garden, so new CU time.
Determined that the fish will be fine for a few hours during the chage.
However, the inspector managed to completely miss a garden garage with electrics, run in Pyro from somewhere...Any one able to guesstimate the sizing from the photo?
And also didn't look in the external meter cabinet it seems - and missed this rather nasty gaping wound in the fuse head. (With DNO for action)