Hair cutting the cores to remove strands also reduces the current carrying capacity of the cable so I would not worry to much about using a reducing pin as it will have less effect than cutting off one of the strands of a core.
For example jointingtech has reducing pins for 70mm² cable that have a reduced pin diameter of 8mm.
From this A=r²π = (8/2)²*3.14159 = 50.3mm²
so your CCC has perhaps changed from 232A to 184A (sp ref C multicore) for a 100A protective device, no real problem there.
The client wants these lugging so this is required even if there’s no real issue
 
No, hair cutting the cable is the problem, the solution is to use reducing pins.
There is an issue with the hair cut, there is not an issue with the reducing pins.
It may be possible to prove the hair cut is not detrimental but it is bad practice and could have caused damage to other strands and further weaken the cable.
 
No, hair cutting the cable is the problem, the solution is to use reducing pins.
There is an issue with the hair cut, there is not an issue with the reducing pins.
It may be possible to prove the hair cut is not detrimental but it is bad practice and could have caused damage to other strands and further weaken the cable.
Sorry I misread what you said.

Thanks for the advise
 

Reply to Recducing pins/lugs in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top