5 5.6Over-current protective device rating exceeds the current carrying capacity of the circuit, feeding multiple outlets / accessories. See Regulations 433.1.1; 533.2.
the electrician is stating you need full rewring and I dont think this is the case. can anyone help and advised what would be the solution to the problem
 
Is that the only code that was given?

Seems simple enough to downgrade the ocpd just to solve this one issue.


"A full rewire" suggests there are other issues have been brought up where repair just isnt enough.

how old is this installation? how old is the fuseboard/ consumer unit?
 
5 5.6Over-current protective device rating exceeds the current carrying capacity of the circuit, feeding multiple outlets / accessories. See Regulations 433.1.1; 533.2.
the electrician is stating you need full rewring and I dont think this is the case. can anyone help and advised what would be the solution to the problem
Unless you post the electric report with names, addresses etc redacted what you have posted is meaningless
 
Not necessarily, it might be that the OCPD is correct for the load and the circuit needs to be rewired because the cable is undersized.
thats not what was stated though... they say the ocpd exceeds the ccc of the circuit... which to me means the cable. Loads can be disconnected/ unplugged... Still leaves a ocpd bigger than the ccc.

Either way.... its not right and needs addressed..... but this one comment on an eicr on its own does not mean the whole place needs a FULL rewire..... (as OP says).... but maybe just this one circuit ??


We need a heck of a lot more information.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
pe3 9pz
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
If other, please explain
n.a
Business Name
n.a

Thread Information

Title
Received Electirc report and states
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
mohammed mustafa,
Last reply from
littlespark,
Replies
4
Views
582

Advert

TrueNAS JBOD Storage Server

Back
Top