Relevance of Table 41.3 where Additional Protection is present? | on ElectriciansForums

Discuss Relevance of Table 41.3 where Additional Protection is present? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
Nov 10, 2022
Messages
16
Reaction score
13
Location
Witney
Reading of 411.3.2 and following suggests that compliance for disconnection <400ms may be obtained using either MCB or RCD. Where an RCD (RCBO in this case) is used for Additional Protection, is compliance with Zs specified in Table 41.3 still necessary?
The situation: new installation by A.N.Other in a timber shower/toilet block on a camping facility. Initially 8 no. hand dryers on a B20 wired in 2.5 T&E radial, 1.25mm flex drops from local FCU to each dryer. Repeated tripping found even with only a single dryer activated led to installer converting radial to ring, protected by C32/r30mA RCBO, and moving 2 of the dryers to a different circuit. The tripping persisted. When I was asked to look at it, I was unable to identify cause of tripping, as nothing showed up in any tests. I concluded it to be an initial burn-in problem, as no more tripping was reported after a couple of months in service.
The problem: while rectifying other poor work, I found the highest R1+R2 reading at the most remote dryer to be 0.51Ω, which with Ze of 0.42Ω puts the Zs well above the Table 41.3 limit for a C32 device.
The question: does this matter?
Thanks for your thoughts.
 
Should we not take into account the possibility/probability of the RCD mechanism going 'sticky', as we all know they can, in which case the 400ms disconnection time would not be achieved?
 
I was more thinking why a C curve breaker , a 32 is most likely needed in case all get put on together, but the motor is probably not much of the load ,so i would guess not too much inrush current to require a C device, you could measure with a clamp meter with a max functon to test this
 
Reading of 411.3.2 and following suggests that compliance for disconnection <400ms may be obtained using either MCB or RCD. Where an RCD (RCBO in this case) is used for Additional Protection, is compliance with Zs specified in Table 41.3 still necessary?
The situation: new installation by A.N.Other in a timber shower/toilet block on a camping facility. Initially 8 no. hand dryers on a B20 wired in 2.5 T&E radial, 1.25mm flex drops from local FCU to each dryer. Repeated tripping found even with only a single dryer activated led to installer converting radial to ring, protected by C32/r30mA RCBO, and moving 2 of the dryers to a different circuit. The tripping persisted. When I was asked to look at it, I was unable to identify cause of tripping, as nothing showed up in any tests. I concluded it to be an initial burn-in problem, as no more tripping was reported after a couple of months in service.
The problem: while rectifying other poor work, I found the highest R1+R2 reading at the most remote dryer to be 0.51Ω, which with Ze of 0.42Ω puts the Zs well above the Table 41.3 limit for a C32 device.
The question: does this matter?
Thanks for your thoughts.
If I encountered this on an EICR I’d still code it as a C3. It is technically compliant, however the Zs exceeding the MCB type and rating is just bad design.
Having said that I’ve rectified many a C2 for high Zs by changing to an RCBO.

Would the loads allow for a reduction to a C20?
 
Bad design or what you are dealt with. I need a type D 32A circuit but the Zs the DB I am connecting to is 0.40. My design is sound but I have to deal with what I have you could not Code it, ADS is satisfied with an RCBO.
 

Reply to Relevance of Table 41.3 where Additional Protection is present? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top