A builder has asked for a quote for rewiring a domestic property all very straight forward until he mentioned relocating the consumer unit to another part of the house with a run of 10m to the new location. TNC-S at orgin.

Looking at options to make this as painless as possible. Thoughts on the different solutions?

Option 1 (no mechanical protection of cable run, in plaster and under floor boards)
Small metal clad unit with DP 100A main switch, 80A 100maRCD 2 pole with 16mm Double insulated meter tails to new consumer unit. Separate 16mm earth. Current rating 87A Consumer unit fitted with RCBO type A

Option 2
Small metal clad unit DP 100A main switch, 80A MCB with 16mm 3 core SWA -banjo on supply end, Current rating 94A. Consumer unit fitted with RCBO type A

So far these are the 2 options i'm looking at to provide necessary protection to the extended tails -
are there any options to use 25mm cable as I don't think 25mm fits into most MCBs and neutral bars unless you know of a brand that would.

Many thanks
 
I would not use an rcd or rcbo , which means it will have to be armoured cable fed from a dedicated switch fuse with isolator.
if they are buried in a wall you need a 30 ma RCD for additional protection or earthed mettalic screen .
 
Do what the last sparks did on a house I’m working on. recently relocated a board due to an extension.
wired in 2 x 2.5 twin a earth connected in parspell directly from the meter then under the suspended floor , along about 15-16 metres , then chased up the wall into a new 18th ed board.

lovely jubbly
 
I am somewhat surprised and concerned at your option one, which is very obviously non compliant.
Thanks for pointing that out Radiohead _ I believe I missed including a OCPD in the brief for option 1.

(From my understanding 411.3.2.3 states 5s disconnection is acceptable for a distribution circuit, without mechanical protection the supply to the sub main would require RCD protection and a MCB.)

123 not sure why you mentioned MCB up front isn't great? Even with SWA you cannot use DNO fuse as your cutout and need to supply a overcurrent device?

Many thanks
 
Thanks for pointing that out Radiohead _ I believe I missed including a OCPD in the brief for option 1.

(From my understanding 411.3.2.3 states 5s disconnection is acceptable for a distribution circuit, without mechanical protection the supply to the sub main would require RCD protection and a MCB.)

123 not sure why you mentioned MCB up front isn't great? Even with SWA you cannot use DNO fuse as your cutout and need to supply a overcurrent device?

Many thanks

I think 123 means why you would use an upfront MCB rather than an upfront fuse.
 
The problem with an up-front MCB is poor selectivity with any MCB/RCBO in the CU. Basically any fault that hits the magnetic trip point will take out the whole supply, and for a 63A C-curve MCB that can be as low as a 0.32kA fault.

Unless you can be sure the tails are not going to be < 50mm from any surface you end up needing RCD protection at 30mA, which again is a selectivity problem.

So the best option is generally a fused-switch feeding SWA, has better selectivity on over-current faults and no need for up-front RCD (unless a TT system).

If going for 63A or 80A fuse / overall limit then 16mm SWA ought to be fine.
 
The problem with an up-front MCB is poor selectivity with any MCB/RCBO in the CU. Basically any fault that hits the magnetic trip point will take out the whole supply, and for a 63A C-curve MCB that can be as low as a 0.32kA fault.

Unless you can be sure the tails are not going to be < 50mm from any surface you end up needing RCD protection at 30mA, which again is a selectivity problem.

So the best option is generally a fused-switch feeding SWA, has better selectivity on over-current faults and no need for up-front RCD (unless a TT system).

If going for 63A or 80A fuse / overall limit then 16mm SWA ought to be fine.
That’s great thank you for clearing that up - in all honesty I never thought there would be selectivity issue between a 63A MCB on the supply end and the rcbos in the consumer unit - it’s a good day when you learn something new - thank you
 
For overload there is no real selectivity problem between MCB if you have something like a 1:1.6 ratio (say 40A & 63A etc) as the down-stream thermal trip will always go first.

The problem with the magnetic trip is often both MCB's coils can be underway to tripping before either disconnects, so they both fire on the fault. Sometimes you can get acceptable behaviour depending on the chosen MCBs and circuit Zs values, and companies often have tables of selectivity limits for MCB/MCB or MCB/RCBO, etc to allow you check this.

You get fancy MCCB with electronic adjustable trip curves that have a short delay option to give you better selectivity, but they cost far more than a fuse-switch and really are not justifiable for domestic work.
 
You get fancy MCCB with electronic adjustable trip curves that have a short delay option to give you better selectivity, but they cost far more than a fuse-switch and really are not justifiable for domestic work.
I had to do just this on a job recently - had to put an upfront adjustable ELCB/MCCB inbetween the incomer and a Ryefield..... ÂŁ800 to Mr Schneider later....
 

Reply to Relocating Consumer Unit to new location in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top