Relocating Consumer Unit to new location | Page 2 | on ElectriciansForums

Discuss Relocating Consumer Unit to new location in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 8, 2010
Messages
83
Reaction score
17
Location
Egham Surrey
A builder has asked for a quote for rewiring a domestic property all very straight forward until he mentioned relocating the consumer unit to another part of the house with a run of 10m to the new location. TNC-S at orgin.

Looking at options to make this as painless as possible. Thoughts on the different solutions?

Option 1 (no mechanical protection of cable run, in plaster and under floor boards)
Small metal clad unit with DP 100A main switch, 80A 100maRCD 2 pole with 16mm Double insulated meter tails to new consumer unit. Separate 16mm earth. Current rating 87A Consumer unit fitted with RCBO type A

Option 2
Small metal clad unit DP 100A main switch, 80A MCB with 16mm 3 core SWA -banjo on supply end, Current rating 94A. Consumer unit fitted with RCBO type A

So far these are the 2 options i'm looking at to provide necessary protection to the extended tails -
are there any options to use 25mm cable as I don't think 25mm fits into most MCBs and neutral bars unless you know of a brand that would.

Many thanks
 
Before heading off for the night, was going to add a last comment that if you ever find no reasonable option other than a MCB feeding a sub-main, say it is coming out of an existing DB or similar, then you generally want the supply MCB to have as high a trip point as you can get away with.

Typically that means going to a D-curve breaker and as high a current as you can meet either both:
  • sub-main overload protection (if load not otherwise limited)
  • end of sub-main Zs for 5s disconnection
Appendix B of the on-site guide is your friend here, as you can see 5s Zs for MCBs on page 131, or for a fused switch on pages 128 (industrial BS88-2 style fuses) or 129 (domestic style fuses BS88-3 similar to BS1361 on following page). Fuses are usually better as well for this, for example, some Zs values:
  • 63A BS88-2 fuse = 0.62 ohm
  • 63A BS88-3 fuse = 0.55 ohm
  • 63A D-curve MCB = 0.28 ohm
You don't see 5s values for C or B curve MCBs as they reach the "instant" trip before the thermal curve gets down to 5s. While selectivity varies a lot from make to make and model to model, taking a couple of examples from the Hager commercial catalogue Jan 2020 that I happen to have on hand:
  • 63A BS88 fuse feeding 32A B-curve RCBO fault limit = 1.5kA (page 133)
  • 63A D-curve MCB feeding 32A B-curve RCBO = 0.80kA (page 136)
  • 63A C-curve MCB feeding 32A B-curve RCBO = 0.51kA
  • 63A B-curve MCB feeding 32A B-curve RCBO = 0.27kA
So you see the fuse has both twice the selectivity of the D-curve MCB and usable with double the Zs!

Also you see for the B and to some extent C-curve MCB feeds the fault level needed to trip it is easily managed by a typical RFC or modest length radial circuit.
 
Before heading off for the night, was going to add a last comment that if you ever find no reasonable option other than a MCB feeding a sub-main, say it is coming out of an existing DB or similar, then you generally want the supply MCB to have as high a trip point as you can get away with.

Typically that means going to a D-curve breaker and as high a current as you can meet either both:
  • sub-main overload protection (if load not otherwise limited)
  • end of sub-main Zs for 5s disconnection
Appendix B of the on-site guide is your friend here, as you can see 5s Zs for MCBs on page 131, or for a fused switch on pages 128 (industrial BS88-2 style fuses) or 129 (domestic style fuses BS88-3 similar to BS1361 on following page). Fuses are usually better as well for this, for example, some Zs values:
  • 63A BS88-2 fuse = 0.62 ohm
  • 63A BS88-3 fuse = 0.55 ohm
  • 63A D-curve MCB = 0.28 ohm
You don't see 5s values for C or B curve MCBs as they reach the "instant" trip before the thermal curve gets down to 5s. While selectivity varies a lot from make to make and model to model, taking a couple of examples from the Hager commercial catalogue Jan 2020 that I happen to have on hand:
  • 63A BS88 fuse feeding 32A B-curve RCBO fault limit = 1.5kA (page 133)
  • 63A D-curve MCB feeding 32A B-curve RCBO = 0.80kA (page 136)
  • 63A C-curve MCB feeding 32A B-curve RCBO = 0.51kA
  • 63A B-curve MCB feeding 32A B-curve RCBO = 0.27kA
So you see the fuse has both twice the selectivity of the D-curve MCB and usable with double the Zs!

Also you see for the B and to some extent C-curve MCB feeds the fault level needed to trip it is easily managed by a typical RFC or modest length radial circuit.
Thank you for the very in depth answer appreciated ?
 

Reply to Relocating Consumer Unit to new location in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top