A builder has asked for a quote for rewiring a domestic property all very straight forward until he mentioned relocating the consumer unit to another part of the house with a run of 10m to the new location. TNC-S at orgin.

Looking at options to make this as painless as possible. Thoughts on the different solutions?

Option 1 (no mechanical protection of cable run, in plaster and under floor boards)
Small metal clad unit with DP 100A main switch, 80A 100maRCD 2 pole with 16mm Double insulated meter tails to new consumer unit. Separate 16mm earth. Current rating 87A Consumer unit fitted with RCBO type A

Option 2
Small metal clad unit DP 100A main switch, 80A MCB with 16mm 3 core SWA -banjo on supply end, Current rating 94A. Consumer unit fitted with RCBO type A

So far these are the 2 options i'm looking at to provide necessary protection to the extended tails -
are there any options to use 25mm cable as I don't think 25mm fits into most MCBs and neutral bars unless you know of a brand that would.

Many thanks
 
Before heading off for the night, was going to add a last comment that if you ever find no reasonable option other than a MCB feeding a sub-main, say it is coming out of an existing DB or similar, then you generally want the supply MCB to have as high a trip point as you can get away with.

Typically that means going to a D-curve breaker and as high a current as you can meet either both:
  • sub-main overload protection (if load not otherwise limited)
  • end of sub-main Zs for 5s disconnection
Appendix B of the on-site guide is your friend here, as you can see 5s Zs for MCBs on page 131, or for a fused switch on pages 128 (industrial BS88-2 style fuses) or 129 (domestic style fuses BS88-3 similar to BS1361 on following page). Fuses are usually better as well for this, for example, some Zs values:
  • 63A BS88-2 fuse = 0.62 ohm
  • 63A BS88-3 fuse = 0.55 ohm
  • 63A D-curve MCB = 0.28 ohm
You don't see 5s values for C or B curve MCBs as they reach the "instant" trip before the thermal curve gets down to 5s. While selectivity varies a lot from make to make and model to model, taking a couple of examples from the Hager commercial catalogue Jan 2020 that I happen to have on hand:
  • 63A BS88 fuse feeding 32A B-curve RCBO fault limit = 1.5kA (page 133)
  • 63A D-curve MCB feeding 32A B-curve RCBO = 0.80kA (page 136)
  • 63A C-curve MCB feeding 32A B-curve RCBO = 0.51kA
  • 63A B-curve MCB feeding 32A B-curve RCBO = 0.27kA
So you see the fuse has both twice the selectivity of the D-curve MCB and usable with double the Zs!

Also you see for the B and to some extent C-curve MCB feeds the fault level needed to trip it is easily managed by a typical RFC or modest length radial circuit.
 
Before heading off for the night, was going to add a last comment that if you ever find no reasonable option other than a MCB feeding a sub-main, say it is coming out of an existing DB or similar, then you generally want the supply MCB to have as high a trip point as you can get away with.

Typically that means going to a D-curve breaker and as high a current as you can meet either both:
  • sub-main overload protection (if load not otherwise limited)
  • end of sub-main Zs for 5s disconnection
Appendix B of the on-site guide is your friend here, as you can see 5s Zs for MCBs on page 131, or for a fused switch on pages 128 (industrial BS88-2 style fuses) or 129 (domestic style fuses BS88-3 similar to BS1361 on following page). Fuses are usually better as well for this, for example, some Zs values:
  • 63A BS88-2 fuse = 0.62 ohm
  • 63A BS88-3 fuse = 0.55 ohm
  • 63A D-curve MCB = 0.28 ohm
You don't see 5s values for C or B curve MCBs as they reach the "instant" trip before the thermal curve gets down to 5s. While selectivity varies a lot from make to make and model to model, taking a couple of examples from the Hager commercial catalogue Jan 2020 that I happen to have on hand:
  • 63A BS88 fuse feeding 32A B-curve RCBO fault limit = 1.5kA (page 133)
  • 63A D-curve MCB feeding 32A B-curve RCBO = 0.80kA (page 136)
  • 63A C-curve MCB feeding 32A B-curve RCBO = 0.51kA
  • 63A B-curve MCB feeding 32A B-curve RCBO = 0.27kA
So you see the fuse has both twice the selectivity of the D-curve MCB and usable with double the Zs!

Also you see for the B and to some extent C-curve MCB feeds the fault level needed to trip it is easily managed by a typical RFC or modest length radial circuit.
Thank you for the very in depth answer appreciated ?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Egham Surrey
Website
https://www.rgpowerservices.com
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
RG Power services

Thread Information

Title
Relocating Consumer Unit to new location
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
richardg,
Last reply from
richardg,
Replies
16
Views
4,761

Advert

Back
Top