Mine's the HD.
Mine's the HD.
I think I'll have to install one on my own home and monitor it.
I'd love to see some more real world data to back up manufacturers' claims though. (perhaps from someone that doesn't immediately lose their chin when you ask them for it....)
I can not see why you had any tripping issues, as they are fitted upstream and just drop the incoming voltage down from (in the case of the one I have fitted) from 245v to 220v.
It is running a GSHP and garage block and is working fine.
Maybe there was a fault in the house and the voltage change caused the RCD to trip?
Do you have rcd protected circuits in the distribution board
Where was your PV connected? Before or after the Voltis.A FAULT!!! how could that be when the rcd didnt trip previously, the solar circuit didnt go on the rcd side either you can call marshall tuflex they may be able to shed some light on why there units are tripping rcds
I think that we may have found the problem, the PV must be connected in before the Voltis unit, as your PV was on a spare way it was connected after the Voltis unit.
That would trip the RCD as the PV would be trying to export back through the transformer in the Voltis unit.
It should be Incoming meter>PV system>Voltis unit>CU.
I hope that makes sense and helps also.