Tomorrow I’m changing my consumer unit in preparation for my NICEIC assessment on 13th November and have a few queries.

Firstly, current cu only has 4 circuits sockets up & down and lights up & down, so hopefully a pretty straight forward swap.

I can unplug 95% of loads on both ring finals, except for the oven and the boiler, both of which have LCD/LED displays. So when it comes to doing the insulation resistance test, would the 500v dc test damage either of these appliances LCD’s or LED’s? The oven and hob ignitor are connected behind the kitchen units.

Also, upstairs we have GU10 spot lights on the landing and bathroom, can’t remove them to do the R1+R2 test as they’re very tight and as we only rent, I can’t cause any damage to the ceiling. So would it be ok to just do the R1+R2 on the final light fitting in the rear bedroom or should I try to find the spots wiring in the loft?
 
I can unplug 95% of loads on both ring finals, except for the oven and the boiler, both of which have LCD/LED displays. So when it comes to doing the insulation resistance test, would the 500v dc test damage either of these appliances LCD’s or LED’s? The oven and hob ignitor are connected behind the kitchen units.

If they have isolators, turn them off and run the full suite of tests (L-N, L-E and N-E). If they don't have isolators join L+N at the board and test L+N to E. This is acceptable when making alterations to existing installations. You just put a LIM in the live-live column for IR.

Also, upstairs we have GU10 spot lights on the landing and bathroom, can’t remove them to do the R1+R2 test as they’re very tight and as we only rent, I can’t cause any damage to the ceiling. So would it be ok to just do the R1+R2 on the final light fitting in the rear bedroom or should I try to find the spots wiring in the loft?

Can you access the loft? If so, do the tests from above. It's nice to verify CPC continuity through out, so at the very minimum I would check R2 at each location using a wander lead.
 
If they have isolators, turn them off and run the full suite of tests (L-N, L-E and N-E). If they don't have isolators join L+N at the board and test L+N to E. This is acceptable when making alterations to existing installations. You just put a LIM in the live-live column for IR.

Can you access the loft? If so, do the tests from above. It's nice to verify CPC continuity through out, so at the very minimum I would check R2 at each location using a wander lead.

Unfortunately neither appliance has an isolator, but thanks for the L+N to E tip.

I have access to the loft, but not boarded out, so will have to be extra careful up there.
 
if you only have 4 circuits, i'd fit a BG 6 way RCBO board with 4 RCBOs .get gear from TLC the BG compact RCBOs are ony £15.60 inc. vat each.

I’ve already bought an MK 12 module board, which leaves 4 modules for future additions.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Fitzy

Arms
-
Joined
Location
Redhill
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
DF Electrical Services

Thread Information

Title
Replacing Consumer Unit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
53
Unsolved
--

Advert

Thread statistics

Created
Fitzy,
Last reply from
Jimmer84,
Replies
53
Views
6,833

Advert

Back
Top