Replacing Consumer Unit | Page 4 | on ElectriciansForums

Discuss Replacing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Fitzy

-
Arms
Joined
Mar 23, 2018
Messages
239
Reaction score
276
Location
Redhill
Tomorrow I’m changing my consumer unit in preparation for my NICEIC assessment on 13th November and have a few queries.

Firstly, current cu only has 4 circuits sockets up & down and lights up & down, so hopefully a pretty straight forward swap.

I can unplug 95% of loads on both ring finals, except for the oven and the boiler, both of which have LCD/LED displays. So when it comes to doing the insulation resistance test, would the 500v dc test damage either of these appliances LCD’s or LED’s? The oven and hob ignitor are connected behind the kitchen units.

Also, upstairs we have GU10 spot lights on the landing and bathroom, can’t remove them to do the R1+R2 test as they’re very tight and as we only rent, I can’t cause any damage to the ceiling. So would it be ok to just do the R1+R2 on the final light fitting in the rear bedroom or should I try to find the spots wiring in the loft?
 
If it passes IR & Zs tests and there are no C1 or 2s, why shouldn't he do a CU change?

The IR test was a pass at >999MOhms and Zs tests are all within range.

Just one query though.....Is it best practice to measure Zs on lighting circuits or calculate the value using Zs= Ze + R1+R2?

I can either for my test results sheet.
 
If it passes IR & Zs tests and there are no C1 or 2s, why shouldn't he do a CU change?

The IR test was a pass at >999MOhms and Zs tests are all within range.

Just one query though.....Is it best practice to measure Zs on lighting circuits or calculate the value using Zs= Ze + R1+R2?

I can either for my test results sheet.
 
Please explain “you’ve broken all the rules with this effort?”

1st and biggest issue is not completing a EICR Before you stated.
A consumer unit change can be done if the original board is in distress. You are able to connect the installation back as is without modification ( if code 1 free).
The catalogue of problems you have listed in this thread after the work leads me to believe your inexperience in doing such work has you struggling to fix the issues
Zs readings prove that the fuse or breaker will operate under fault conditions - IT DOES MOT PROVE COMPLIANCE WITH THE OTHER PAGES ON THE BOOK. Installation methods, accessibility of connections, access to switches to isolate for maintenance etc. This comes with experience over time. EICR are to prove the installation is safe for continued use NOT just to check Zs
 
Please explain “you’ve broken all the rules with this effort?”

1st and biggest issue is not completing a EICR Before you stated.
A consumer unit change can be done if the original board is in distress. You are able to connect the installation back as is without modification ( if code 1 free).
The catalogue of problems you have listed in this thread after the work leads me to believe your inexperience in doing such work has you struggling to fix the issues
Zs readings prove that the fuse or breaker will operate under fault conditions - IT DOES MOT PROVE COMPLIANCE WITH THE OTHER PAGES ON THE BOOK. Installation methods, accessibility of connections, access to switches to isolate for maintenance etc. This comes with experience over time. EICR are to prove the installation is safe for continued use NOT just to check Zs

If it had been a customers board change I may have done an EICR beforehand, but at present an EICR is NOT a reg or compulsory before changing a cu, so it’s up to the electricians discretion if one is carried out or not!

There are timed served electricians on this very forum that haven’t carried out an EICR before a customers board change (mainly because customers won’t pay for one), but they’ve STILL carried out the board change and found plenty of faults afterwards which the customers won’t pay to rectify, but as has been said on here before, the electrician changing the board is responsible for the board change only and NOT the entire installation (barring any C1 codes).

I’m learning, so fixing the issues which arose from my own board change is a way to learn without inconveniencing or charging a customer a fortune for the privilege. I’ve learnt plenty from doing this board change and have thoroughly enjoyed the learning experience.

I appreciate your comments though. ;) ;) ;)
 
but as has been said on here before, the electrician changing the board is responsible for the board change only and NOT the entire installation

Not So! The electrician 'is' responsible for making sure the existing circuits are safe to re-energise when a CU is changed.
The fact that say, just because an existing ring is open circuit before the board is changed doesn't make it right to reconnect it onto a new 32A MCB.
Final circuits should be inspected (as much as physically possible) and tested 'Prior' to re-terminating to ensure they are safe to re-energise.
 
Fitzy,

You sound like you’re doing a great job mate, got your head screwed on regarding most of what you are saying, and asking questions is the key.

As much as a customer may not want to pay for an eicr, DefyG is correct in what he’s saying with regards to the responsibility YOU take upon issuing the EIC once you have completed the work.

I always make sure that I carry out a Ze, IPF, IR and ring test, as well as checking the main bonding when I turn up to quote the job.

I then advise the customer of anything that may affect me issuing the EIC upon completion and get them to agree to the works.

If you know what you’re taking about and can speak to people, then I find the customer always has the additional work done, and are happy for the info....
 

Reply to Replacing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
380
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
867

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top