Hi, Just recently qualified.
I've replaced some old 32amp junction boxes under the floor in my landing with Wago and Wago boxes to make them maintenance free prior to putting down new flooring.
Prior to doing this, i tested the ring continuity, r1 was 0.52 ohms, rn was 0.53 and r2 was 0.73, so was well within the 1.67 reg, now when i tested the ring once the work was complete the readings are: r1 0.47, rn 0.48 and r2 0.99 ohms. I have double checked all connections, but the r2 reading still seems a little high and doesn't meet the 1.67 guideline. I/R tests are fine. Maximum Zs is 0.54 ohms but that is on a dropdown spur to the lounge from the ring upstairs.
The reason i changed them was that there was no earth sleeving present and the terminals where not tight and could not be tightened.
I know the Wagos will introduce more resistance but just wanted to check what you guys thought.
Timmo.
I've replaced some old 32amp junction boxes under the floor in my landing with Wago and Wago boxes to make them maintenance free prior to putting down new flooring.
Prior to doing this, i tested the ring continuity, r1 was 0.52 ohms, rn was 0.53 and r2 was 0.73, so was well within the 1.67 reg, now when i tested the ring once the work was complete the readings are: r1 0.47, rn 0.48 and r2 0.99 ohms. I have double checked all connections, but the r2 reading still seems a little high and doesn't meet the 1.67 guideline. I/R tests are fine. Maximum Zs is 0.54 ohms but that is on a dropdown spur to the lounge from the ring upstairs.
The reason i changed them was that there was no earth sleeving present and the terminals where not tight and could not be tightened.
I know the Wagos will introduce more resistance but just wanted to check what you guys thought.
Timmo.