I have I have about an 800 foot run. What would it take to get adequate amperage and voltage at the end of that for 120v 30 to 50 amps?
 
I looked that up it's $2900 for 500 feet and I need 3200 ft 4x800 which equates to $18k that's insane
I’ll tell you what why don’t you buy # 8 and run that 800 feet and put 50 amps and see how that works for you. There is a formula for voltage drop, look that up and see what size wire you need for that. Insane is pulling 800 feet of wire just for 120vac. Buy a generator and see how that works for you
 
I’ll tell you what why don’t you buy # 8 and run that 800 feet and put 50 amps and see how that works for you. There is a formula for voltage drop, look that up and see what size wire you need for that. Insane is pulling 800 feet of wire just for 120vac. Buy a generator and see how that works for you
No to be a dick or anyting that's just a crazy amount of money was all I was saying geez it's how you talk to everybody?
 
Remember that cable size can be reduced if the current is lower.
It may be possible to run 240v down to a transformer to make your 110v near to where it is used.
 

Reply to requirements for a long run in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
384

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top