T

thekingiam

was looking at a tt cu and the main earth goes outside into a concrete driveway cable looks quite small, is the minimum cable size requirement the same as other earthing arangements?
if i do need to replace, would i need to provide inspection pit.
its being protected by a rcd,could i use rcd as means of isolation while changing cu?.
testing earthing arangement could i do earh loop test on my multimeter instead of having to buy electrode tester?
 
Here we go again, lol.
Page 41 of the Green OSG table 4.4(ii)
2.5mm min size when protected against corrosion and mechanical damage, ie sheathed and in conduit, buried or not buried.

The figure in dispute is the 4mm for not buried but protected/not protected against corrosion. Clearly stated in the OSG but no reference to it in the regs...
 
but my argument was why the hell does the pic in the OSG show 16mm CSA.....as if that CSA will make much difference to a TT earthing arrangement...lol....


Depends doesn't it, ...if were talking about the numbty 200 ohms as mentioned in BS7671 then your probably correct...lol!! But if you (god forbid) managed to install a decent TT system and got the Ra down to 1 ohm or even sub ohm value, then a 10/16mm earthing conductor from the earth electrode(s) would be quite prudent!! lol!!
 
If your running out a sub main to a garage on a TT system is there any issues with spiking the board in the garage as well as the main spike at source ?

None whatsoever, in fact it would be prudent to do so!! The more earth rods or positions on a TT system the better!!

Link the 2 earth rod positions either using the SWA of your sub-main cable, or by a separate conductor to the MET via the EMT of your garage CU....
 

Reply to requirements for tt earthing? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
696
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
658
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top