I recently had the house (3 bed semi) rewired and have come across some things that are causing me concern. I’ve made the Electricuan aware but have not yet had a proper response so I just want to get some alternative “expert” opinion.
Basically three issues.
1. The upstairs and downstairs sockets are now fed by an MCB, Type B rated 16A. I’m of the opinion these are probably too small and should be at least 20 if not 32A? For info we have 16 x 13A sockets downstairs alone. The reason ( I think) for it being 16A is explained below.
2. Downstairs, instead of rewiring a 60 year old property as a ring main, the Electrician has connected the sockets as radial spurs and fed them with 2.5mm cables from the ceiling void. Hence, I think, the reason why the breaker is only 16A? I don’t know why they were not run as a ring but shouldn’t the cable be at least 4mm, thus allowing a biggger MCB?
3. There was a single 13A socket which we had an extension block connected too, feeding tv, sky box, dvd etc. I wanted this changing to 4 new sockets (two doubles) to get rid of the extension block. The Electrician has also wired this as a spur and a spur off a spur, all run again in 2.5mm.
What are your thoughts on this and what would be your advice?
Basically three issues.
1. The upstairs and downstairs sockets are now fed by an MCB, Type B rated 16A. I’m of the opinion these are probably too small and should be at least 20 if not 32A? For info we have 16 x 13A sockets downstairs alone. The reason ( I think) for it being 16A is explained below.
2. Downstairs, instead of rewiring a 60 year old property as a ring main, the Electrician has connected the sockets as radial spurs and fed them with 2.5mm cables from the ceiling void. Hence, I think, the reason why the breaker is only 16A? I don’t know why they were not run as a ring but shouldn’t the cable be at least 4mm, thus allowing a biggger MCB?
3. There was a single 13A socket which we had an extension block connected too, feeding tv, sky box, dvd etc. I wanted this changing to 4 new sockets (two doubles) to get rid of the extension block. The Electrician has also wired this as a spur and a spur off a spur, all run again in 2.5mm.
What are your thoughts on this and what would be your advice?