Found myself in a bit of a predicament
Carrying out a PIR in a factory
Testing an existing ring circuit in an industrial distribution board which must be nigh on 35 - 40 years old, asbestos flash guards and all!
The problem with that the DB does not have cpc terminals, and all the cpc's are twisted together and then looping around and fixed via the one available earthing nut at the DB
I carried out the ring tests on phase and neutral which returned satisfactory results of around the 0.75 ohm mark each.
Now to test the cpc's I would have to disconnect every cpc to untwist them all from each other and find the correct cpcs and carrying out the test.
Because of this reason I informed the supervisor that the entire DB would have to be isolated as there would be no cpcs connected.
Low and behold the supervisor had a week earlier tested a similar DB about 20 metres away, exactly the same scenario. He carried out the tests live and spent an entire day disconnecting all the cpc, finding the correct ones, testing and then reconnecting them.
The DBs are due to be upgraded anyway by the way, and the ring tests could be confirmed then
So anyway after informing him that the entire DB would have to be isolated he said thats fine just go ahead and do it. I told him that I would require adequate lighting as the lights are fed from this DB and he handed me his torch!
So I thought about this a bit more, I had tested the phase and neutral which were satisfactory, I could see the cpc's from the two ring cables were connected to earth, surely I could just go to the middle socket of the ring, split the cpcs and carry out the tests from here
OK, I know that the standard practice is to do this at the DB, but in this particular circumstance, given the amount of time that would be required I decided that, in my professional opinion, I would be happy with this and if the ring was broken there would be no continuity between the two legs.
So I went to the middle socket, split the cpcs and returned a reading of 0.92, which would add up, slightly higher that the L & N given that it is Twin and earth (2.5/1.5)
My supervisor returned to see how I was getting on, I informed him of the way I had carried out the test to which he said thats no use that aint the way you do it. i tried to explain my reasons for doing this including the theory but he was having none of it and it ended with him saying he was going to report me to the big boss for refusing to carry out his procedure.
What do you guys think?
Carrying out a PIR in a factory
Testing an existing ring circuit in an industrial distribution board which must be nigh on 35 - 40 years old, asbestos flash guards and all!
The problem with that the DB does not have cpc terminals, and all the cpc's are twisted together and then looping around and fixed via the one available earthing nut at the DB
I carried out the ring tests on phase and neutral which returned satisfactory results of around the 0.75 ohm mark each.
Now to test the cpc's I would have to disconnect every cpc to untwist them all from each other and find the correct cpcs and carrying out the test.
Because of this reason I informed the supervisor that the entire DB would have to be isolated as there would be no cpcs connected.
Low and behold the supervisor had a week earlier tested a similar DB about 20 metres away, exactly the same scenario. He carried out the tests live and spent an entire day disconnecting all the cpc, finding the correct ones, testing and then reconnecting them.
The DBs are due to be upgraded anyway by the way, and the ring tests could be confirmed then
So anyway after informing him that the entire DB would have to be isolated he said thats fine just go ahead and do it. I told him that I would require adequate lighting as the lights are fed from this DB and he handed me his torch!
So I thought about this a bit more, I had tested the phase and neutral which were satisfactory, I could see the cpc's from the two ring cables were connected to earth, surely I could just go to the middle socket of the ring, split the cpcs and carry out the tests from here
OK, I know that the standard practice is to do this at the DB, but in this particular circumstance, given the amount of time that would be required I decided that, in my professional opinion, I would be happy with this and if the ring was broken there would be no continuity between the two legs.
So I went to the middle socket, split the cpcs and returned a reading of 0.92, which would add up, slightly higher that the L & N given that it is Twin and earth (2.5/1.5)
My supervisor returned to see how I was getting on, I informed him of the way I had carried out the test to which he said thats no use that aint the way you do it. i tried to explain my reasons for doing this including the theory but he was having none of it and it ended with him saying he was going to report me to the big boss for refusing to carry out his procedure.
What do you guys think?