having added a couple of sockets to a ring final circuit when doing end to end tests i have no cpc end to end any advice i have checked my new works and all cpc connections are good could well have already been existing fault any advice welcomed
 
Between a rock and a hard place unfortunately, although the broken CPC isn't the worst thing that it could of been it will still need correcting


You need the habit of pre testing or pre warning customer of possible additional works
 
Last edited by a moderator:
yes i agree this does need correcting have done loop test on all sockets on the ring and all readings well within would have expected unuasual readings due to broken cpc but to no evail
 
Separate legs at consumer unit join l/CPC of one leg together and go round each socket checking for continuity when you lose it your either at break or just passed it

TBH unless you have a very understanding customer, you may have to take this on the chin and learn from it. The customer will no doubt think you are trying to get them to pay for something they should not pay for. "It was fine before you came" they will say even if it wasn't!
 
Last edited by a moderator:
parallel conductors not following the same route contravenes a reg. forgot which one. it's a bit like buses. they follow different routes, but they don't have conductors any more.
 
Hmm, how about finding the original problem and sorting it?

Yes that would be the ideal way forward. I was simply offering an alternative. Provided both legs are connected to the same circuit breaker, then the circuit as a whole is protected by a 20 amp device and so the continuity around the ring is not necessary so any break in no matter which conductor doesn't matter. You can call it whatever you like.
 

Reply to ring continuity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
587
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
765
  • Question
Why aren't you asking them?
Replies
5
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks