nice sums malcom, but can you say lets say you have values for r1 r2 rn... if you designing or longest possible
That is how I work out the length and volt drop in a Ring.
Length
2.5mm T&E ring.
1 conductor 2.5mm CSA @ 7.41mohm/m
1 conductor 1.5mm CSA @ 12.10mohm/m
{from page 166 OSG}
so if you have a measured value of say
r1 @ 0.58/7.41 x 1000 = 78.27m
rn @ 0.58/7.41 x 1000 = 78.27m
r2 @ 0.96/12.10 x 1000 = 79.33m
Volt Drop
Divide the length by 4 = 19.57 x 18 x 26/ 1000 = 9.16v
Bs 7671 pg 258, 6.1 correction for operating temp.
This calculation give you a ct of .923, x 9.16 = 8.45v
or
4 x 8.45v x 1000/26/18 = 72.22 / .923 = 78.24m
It assumes 20 amp at the furthest point and 12 amp distributed evenly around the ring so,
average = (32 + 20)/2 = 26 which is the value that Lenny posted.
I believe it's 10m for 2.5mm² protected by a 32A B type MCB.
That's according to Table 7.1 in the OSG.
Sorry that should be 106m not 10m.
Don't seem to be able to edit it for some reason?
ring design and voltage drop
esc,
i=p/u,