Ive used both ohms law R = V / I and used the values of mohms per meter out of table 4D5 in BS 7671.


From the OSG 2.5 T&E has a resistance of 0.01951 ohms per meter, so R = 0.01951 times m (meters) that is

R = 0.01951 * m

Ive taken V as volt drop at 11.5V and I as 32A, the rating of the PD, giving:


0.01951 * m = 11.5 / 32 ohms law


or m = (11.5 / 32)/0.0195 = 18.43m ??


Using the mV/A/m from table 4D5 of BS 7671, we have a value of 18mV, therefore

(18*32*m)/1000 = 11.5V


or m = 19.96m ??

Ive got this all wrong i know i = p/u. Think my perceptions of how a RFC handles voltage and current is off the scale!! But now ive had a thought from a post earlier.

Is from jamesbrownlive's post above, pg2, and how you both mention about dividing by 4. It would seem logical that when considering a RFC's construction, we have to consider that as a ring the CSA is doubled and the length effectivly halved, which would reduce the resistance to 1/4 of its standard value of 0.0195 ohms per m, in this case that would become 0.004875 ohms per m. Recalculating we have:

0.004875 * m = 11.5 / 32

m = 73.7m
which now seems ample length of cable to construct an A1 ring

What you think?

I think your not far off, you need to make a further consideration to load distribution and conductor temperature and your there.

Regards Chris
 
I use an (Ib) of 26A when calculating for an A1 RFC which would gives a maximum length of 98M.

It can be engineered further but I prefer to err on the side of caution with 26A and (Ct) of 1.
 
Hi spinlondon, i never been taught to use diversity with cable selection. That doing so is is a definite no no. Diversity is applied to maximum demand to give a practical/realistic expectation of the current being drawn off he supply and hence through the service fuse at any one time.
 
Cheers chris. Im trying to get my head around load distribution and the calculations.
Get what you say about conductor temperature.
I've done the calculation without any correction and method C to keep things as simple as possible
 
Hi spinlondon, i never been taught to use diversity with cable selection. That doing so is is a definite no no. Diversity is applied to maximum demand to give a practical/realistic expectation of the current being drawn off he supply and hence through the service fuse at any one time.
Consider then a RFC with 10 socket-outlets.
What CSA of cable would your method indicate, and what rating of CPD would be required?
 
That is how I work out the length and volt drop in a Ring.

Length

2.5mm T&E ring.
1 conductor 2.5mm CSA @ 7.41mohm/m
1 conductor 1.5mm CSA @ 12.10mohm/m
{from page 166 OSG}

so if you have a measured value of say

r1 @ 0.58/7.41 x 1000 = 78.27m
rn @ 0.58/7.41 x 1000 = 78.27m
r2 @ 0.96/12.10 x 1000 = 79.33m

Volt Drop

Divide the length by 4 = 19.57 x 18 x 26/ 1000 = 9.16v

Bs 7671 pg 258, 6.1 correction for operating temp.

This calculation give you a ct of .923, x 9.16 = 8.45v

or

4 x 8.45v x 1000/26/18 = 72.22 / .923 = 78.24m

It assumes 20 amp at the furthest point and 12 amp distributed evenly around the ring so,

average = (32 + 20)/2 = 26 which is the value that Lenny posted.
 
Last edited:
Hi lenny, im with i = p/u. Can we see you full calc
Cheers

Ok, VD will limit the length of your RFC before any other factor. So if we use our max permitted VD of 11.5V in our calc for finding the max permissable length we 'should' arrive at a value within the 5% tolerance.


So (4 x 11.5 x 1000)/(Ib x mV/A/M x Ct) = max permissable length.

= (4 x 11.5 1000)/(26 x 18 x 1) = 98.29M.


As I said it can be engineered further to give a longer length but I personally use the above.
 
Last edited by a moderator:
Cheers for your help spinlondon, things are getting clearer. Have always taken appendix 15 as is, with no explanation of the design behind these circuits. Radial are fine, the ring threw me, so thanks for your help in this matter
esc
 

Reply to ring design and voltage drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
132
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
914
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
390
I'd always go for 25mm2 5core over 50mm2 3core, with the cores paired up. Considerably cheaper, easier to terminate and ready to go, if ever 3...
Replies
7
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top