Hi all had a weird one today, actually make it two, tested ringfinal continuity at the board lives were 0.00 and so were neutrals, earths were the same too, not sure why, is it a ring that has been interconnected causing a duff reading??
Secondingly tested another property's ringfinal circuit and got 30 ohms, very high- across lives an neutrals, earths were 49 ohms.........has anybody discovered similiar readings as i need to put an observation against these results and i would be even happier if i knew what they suggested/what was wrong with these circuits?? :sad_smile:
 
My testers fine, batteries fully charged, and checked readings on my spare meter, exactly the same so the readings are correct, i think the ring is interconnected very close to the board and is duffing the reading up hence the 0.00 which is obviously not a correct/compliant reading as it suggests no resistance............there must be a reason for it

Ok if you think the ring is interconnected close to the board why did you not open a socket at the half way point and test there. I would suspect ring leaving board probably straight to a JB then on to sockets.
 

Reply to Ring final continuity readings............. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top