Ring final & Radial circuits off one mcb ? | Page 4 | on ElectriciansForums

Discuss Ring final & Radial circuits off one mcb ? in the UK Electrical Forum area at ElectriciansForums.net

Soulsurfer

-
Arms
Joined
Feb 21, 2013
Messages
623
Reaction score
143
Location
Channel Islands
Another straight forward job today has turned out to be a right mess once again so I thought I'd get some thoughts on the following before I start !

So an old MK LN59 board, feed to garage sockets on a single 2.5mm t&e from a 15A mcb and also spurred to feed a boiler on S plan,

Next ring final on a 30A feeding upstairs sockets as usual but on cover removal I found a 4mm t&e spurred from same 30A mcb and feeding opposite side of garage to sockets all on the 4mm then at the end spurred from last socket with 2.5mm t&e to feed new water cylinder via a DP switch !

Obviously I'm not happy with the 4mm being spurred as an extra circuit from a separate circuit pd but surely the immersion being spurred from sockets is rough too ?

Never seen anything like that before !
 
Oh the joys of Part P.
Options install a new circuit which has to be notified, or connect to an existing circuit, which doesn't have to be notified.
Options install new CU which has to be notified for new circuit which also has to be notified, or connect to existing circuit which doesn't have to be notified.
All comply with the Wiring Regs. and Statutory requirements, though some options are cheaper than others.
 
Was some time last year when I joined the forum went on for days. I read Reg 314.4 to mean two final circuits should have individual circuit protection and I won't sway from that. In the OPs case and probably nearly every situation like this a new circuit has just been tagged onto an existing circuit even if spare ways are available, to me the intention has been to create a new circuit and by connecting in this manner does not suddenly mean the two circuits now become one. To me this is just poor installation methods.

Would you class smoke detectors and lighting wired separately but on the same OCPD as "poor installation methods"?
 
Was some time last year when I joined the forum went on for days. I read Reg 314.4 to mean two final circuits should have individual circuit protection and I won't sway from that. In the OPs case and probably nearly every situation like this a new circuit has just been tagged onto an existing circuit even if spare ways are available, to me the intention has been to create a new circuit and by connecting in this manner does not suddenly mean the two circuits now become one. To me this is just poor installation methods.

I agree that this is a dodgy job, they may as well have open end up the ring and extended it to serve the new sockets.

But what I am interested to know is how you are defining what is a circuit.
 
Would you class smoke detectors and lighting wired separately but on the same OCPD as "poor installation methods"?
This doesn't phase me (plagarism, sorry) as the cables are likely to be the same size (if I did it :rolleyes:) and IMHO from mcb they form one radial circuit with multiple branches. But the OP's 4mm radial in bed with a 2.5mm rfc at 32A mcb just doesn't seem right to me.
 

Reply to Ring final & Radial circuits off one mcb ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
376
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
336
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
376

Similar threads

  • Question
Why aren't you asking them?
Replies
5
Views
847
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top