Just checking, what I think I already believe.

Doing a pre-install test of some outdoor sockets on a ring final. So far, confirmed bonding, incoming polarity, Ze and Pfc and RCD Test on circuit, everything fine and within regs.

However on testing Ring Final, Line came out fine (0.7), Neutral came out >19.99kOhms, CPC came out as expected (1.67 x Line). Line and CPC were within an expected range, and a live Zs test confirmed those readings (0.32).

So here's the thing. Everything except the Neutral Rn test passed. I did these tests at a socket, not at the board so the Line, Neutral and CPC were still connected, only the ring final circuit was de-energised.

It's likely I have a break in the neutral somewhere, but given I have the ring final connected to the rest of the house in the board, is it possible the neutral reading has been skewed because I'm essentially testing the entire neutral of the house ? Before I go splitting the ring etc, should I disconnect the ring final neutrals at the board, jump and re-test ?

Hope that makes sense.
 
You should disconnect at the board when doing RFC dead testing, this will remove parallel paths etc.
 
with circuit isolated, take the 2 N's out of the N bar in CU then try rN on them. if still over range, you have a break. then if you connect 1 of the N's to it's corresponding cpc, test for Rn+R2 at each socket. soon find the break.
 
Thanks. That's what I thought. So much for a simple Outdoor socket install, and I've got another ring final extension to do tomorrow...joy! Ring Final faults must cost us so much time and money.
 
Thanks. That's what I thought. So much for a simple Outdoor socket install, and I've got another ring final extension to do tomorrow...joy! Ring Final faults must cost us so much time and money.
i consider finding faults to make me money.
 
Well, the client has decided not to pursue the fault, so I've backed away from doing the install. I've put it in writing that there is a fault that needs to be dealt with, so if anything happens subsequently I can't be bitten by it.
 

Reply to Ring Final Test - Neutral >19.99kOhms in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Very technical :D
    • Like
Replies
9
Views
427
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top