That must be total length of cable then. But for sure the OSG also states an A1 RFC is maximum 100sqm floor space.
For a 100sqm room you could be using any length of cable from 20m to over 100m in length, dependant on the route the cable takes etc.
for VD on a spur, I'd estimate the length of cable from one end of the rfc and add the spur length, then use mV/A/m. this would give a pessimistic figure as the VD on the rfc part would be less.
Reply to Ring finals and fused spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...