Evening all. The OSG says "As a rule of thumb for rings, unfused spur lengths should not exceed 1/8 the cable length from the spur to the furthest point of the ring.".

Okay, so what is the maximum length for a fused spur then? I don't seem to be able to find the answer in the OSG or BBB. I assume the limiting factor is voltage drop, but how is this determined?
 
I think we're driving down the wrong road here Charlie. The OSG states that 1/8th rule is for unfused spurs, I want to know the max length of fused spurs. I assume there is a difference, otherwise why would the OSG say 'unfused spurs' rather than just 'spurs'?
 
Ahh sorry didn’t realise you mentioned fused spurs..
Yes as you say it would be down to volt drop for the length of the cable and current
 
That's the problem, determining the volt drop for a spur from a ring. How do you do it? Calculating the voltage drop for the spur bit I can do, but not sure about the ring part.
 
That must be total length of cable then. But for sure the OSG also states an A1 RFC is maximum 100sqm floor space.

For a 100sqm room you could be using any length of cable from 20m to over 100m in length, dependant on the route the cable takes etc.
 
for VD on a spur, I'd estimate the length of cable from one end of the rfc and add the spur length, then use mV/A/m. this would give a pessimistic figure as the VD on the rfc part would be less.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Ring finals and fused spurs
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Thread Tags

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
telectrix,
Replies
16
Views
2,203

Advert

Back
Top