Ring finals and fused spurs

Evening all. The OSG says "As a rule of thumb for rings, unfused spur lengths should not exceed 1/8 the cable length from the spur to the furthest point of the ring.".

Okay, so what is the maximum length for a fused spur then? I don't seem to be able to find the answer in the OSG or BBB. I assume the limiting factor is voltage drop, but how is this determined?
 
I think we're driving down the wrong road here Charlie. The OSG states that 1/8th rule is for unfused spurs, I want to know the max length of fused spurs. I assume there is a difference, otherwise why would the OSG say 'unfused spurs' rather than just 'spurs'?
 
Ahh sorry didn’t realise you mentioned fused spurs..
Yes as you say it would be down to volt drop for the length of the cable and current
 
That's the problem, determining the volt drop for a spur from a ring. How do you do it? Calculating the voltage drop for the spur bit I can do, but not sure about the ring part.
 