Hi All,

While carrying out a commercial EICR today, I was doing IR testing on one of the ring mains an was getting 0.00M ohms between L/N - and the earth bar at 250V & 500V (cant distinguish what 2 earth wires belongs to the other 4 cores)

I have continuity on both L & N legs which are acceptable.
Also tested L- E bar and N - E bar both giving me 0.00M ohms
carried out a resistance test for both L & N to E bar, one was 24.4 ohms and the other was 1034 ohms

No RCD protection at all. TN-S system.

Stumped.... any suggestions on coding and where to start looking for this would be greatly appreciated.
 
Hi Ross.

I know it may sound obvious but did you have the main switch off when you were testing (not just the MCB) as it is TN-S so will be continuity between N and E (and also L-E unless you were sure everything was unplugged?).

If the main switch was open when you tested then I guess you have an earth fault somewhere (commonly a screw in one of the back boxes clipping the neutral). As this is an EICR I would just be coding it and not thinking too much about solving the fault yet (unless you code it C1).
 
Last edited:
Yes HHD, the main switch was open..both lives out of MCB, both neutrals out of the neutral bar. The earths all still in earth bar. I know the likelihood is that the fault is down between both live conductors and their own cpc. All other ring mains were all >500Mohm apart from another which had a reading of 0.40Mohm.

circuit working fine....although no RCD is present. So I'm thinking a C1 or 2
 
What was the actual measured resistance?
0.00M ohm could mean the actual measurement was 999,999ohms.
I'd be inclined to say there is a load still connected, or a neon or PIR somewhere on the circuit.
 
Hi Alanl, the resistances are in my original post. This would surely not be the case though as I was doing IR between live/neutral to earth
 
TNS with the main switch closed would still give a N-E resistance of 0.0MΩ, the connection is just further away (at the sub station).

I would say that you have a 52W piece of electronics still connected.
The smoothing capacitors giving you the 24Ω L-E reading as a false reading and the 52W coming from the difference in the N-E resistance to the L-E resistance, so the N-E is 1010Ω higher i.e. 52W
 

Reply to Ring main IR question from todays EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
359
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top