Ring main no continuity on live ends | Page 2 | on ElectriciansForums

Discuss Ring main no continuity on live ends in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 3, 2019
Messages
37
Reaction score
6
Location
South wales
Hi, Im a bit puzzled, recently did a new kitchen install with complete new wiring from the cu, this included a kitchen ring, upon testing I have continuity on the n to n end amd cpc to cpc but no continuity on the live ends, Insulation resistance checks out fine on investigation using the half test method, so im confused to as why this is?
 
Due to the run of the cable from the cu to the kitchen is restricts me from the r2 method so I was thinking if I connect the line to earth at the db of leg 1 at the board and then use my multifucntion tester with the plug attachment at each socket this should narrow the problem down?
Yeah, that's what I meant. This is the R2 adaptor, it'll save you taking off the sockets:

[automerge]1574629153[/automerge]
Plug adaptor = R2 adaptor, same thing
 
Yeah, that's what I meant. This is the R2 adaptor, it'll save you taking off the sockets:

[automerge]1574629153[/automerge]
Plug adaptor = R2 adaptor, same thing
I get you! Appreciate the response
 
No I totally agree mate, during my apprenticeship I never really came across any fault finding so I have a little experience, also in college we never really went into depth on it so Its the things like this they need to teach more at college, I know you get more from the actual on site experience but if you dont come across it then its not something you will know but I get what youre saying.
[automerge]1574627672[/automerge]
Well you've come across it now.... and it's called on site experience;)
 

Reply to Ring main no continuity on live ends in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top