farmerian

Is there a maximum r1 rn and r2 value for a ring main ?
I no the maximum ZS is 1.10ohms for a 32amp type B curve breaker but is there anything in regs for the end to end resistance of the ring ?
 
Is there a maximum r1 rn and r2 value for a ring main ?
I no the maximum ZS is 1.10ohms for a 32amp type B curve breaker but is there anything in regs for the end to end resistance of the ring ?

Haven't got Yellow OSG with me at the moment, but Table 7.1 (i) of the Green OSG gives some maximum cable lengths for ring circuits with varying protective devices, so in effect giving max r1, rn & r2. I guess the Yellow version values with differ from the Green book due to the new 0.95 factor!
 
Well, I'd say your Zs, so comply would have to be say 1.1 or less, so I suppose the worst case scenario for R1+R2 would have to be no more than 1.1 - 0.35 which would be the lowest out of the supply types.

i suppose this is hypothetical and calculated opposed to measured anyway. So suppose you did that you R1+R2 would have to be no more than 0.75,

im probably totally wrong but I suppose if you were to calculate it on paper for a TNCS supply type I'd say your max figures would be the following based on 2.5/1.5

R1+R2 = 0.75
r1 = 0.56
rn = 0.56
r2 = 0.94

its only a stab in the dark and probably wrong.
 
Recommended max floor area for a RFC is 100m2 iirc. There is no maximum figure for r1,r2 etc as such, as ultimately, it's achieving less than the max Zs which will be the determining factor.
 
Recommended max floor area for a RFC is 100m2 iirc.

That was simply a historical requirement. The 17th Edition removed it so there is no 100m^2 maximum anymore.

As said if the circuit is designed for 0.4 second disconnection and non-excessive voltage drop then that is the limit.
 
and probably wrong.

You're out by a factor of two. The maximum value of r1+r2 cannot be more than 4 times the maximum R1+R2, because the highest resistance will occur halfway round the ring where it is served by two legs of half the total length in parallel, each of (r1+r2)/2.
 
You're out by a factor of two. The maximum value of r1+r2 cannot be more than 4 times the maximum R1+R2, because the highest resistance will occur halfway round the ring where it is served by two legs of half the total length in parallel, each of (r1+r2)/2.

Oh yes, why did i divide it by 4? No idea, I know it's two. Thanks for the correction.

i was on the right lines but out if that makes sense.
 

Reply to Ring Main resistances in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
448
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
276

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top