I recently tested a doctors surgery and found a number of ring mains
are too large. r1 1.9 rn 1.9 r2 2.7. Zs 1.47 supplied from a type 2 32 amp breaker
could anyone suggest how best to rectify this.
Dont really want involved with the remedials but don't usually refuse work.
any of u guys any suggestions
 
thought hes concerned about the high zs reading 20a breaker would be better but your not breaking any reqs installing an rcbo which would allow him a reading of 1667 ohms whats up with that
we know what BS7671 says mate...

but its a load of crap...and needs sortin out....

its a really slovenly way to meet times....

and if the RCD/RCBO fails?
 
I'm not saying it breaks anything that could be used against you in a court, what I am saying is that if anyone seriously thinks that 1667 is an acceptable reading and would happily walk away from it without a second thought then they should not be part of our trade.
Further, Napit and the others don't make the rules.
 
not saying id be happy trev would rather investigate but napit and others say in there brochuers that its acceptable to install rcbo to acheive zs readings what req does it break
the long & short of it is that you should never be having to rely on an RCD device on a well designed circuit coming of a TN

and whoever it is at Napit (the land of the plastic 2391)...wants to have a word with themselves....

it needs sortin out does that one in BS7671....

RCDs for fault...:yes

RCDs as a sole measure to meet times on a TN...:no
 
Good grief!
Hang on a bit, isn't the 1667 only on TTs?
a typical scenareo given is that a cooker circuit`s value of loop is high..

then the class are asked for suggestions on how to `rectify` this...

using an RCD to meet times is one of the acceptable answers...

pulling in a parrallel G/Y is another...
 

Reply to Ring main too big?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top