Just been looking at a rather confusing and disgusting job in a two floor ex-council house and wondering if anyone could give me any ideas (apart from walking away from it).
Just been looking at a rather confusing and disgusting job in a two floor ex-council house and wondering if anyone could give me any ideas (apart from walking away from it).
- The ring has been tripping the RCD (main switch)
- Live and Neutral have both failed IR test to earth
- I split the ring at 4 sockets starting at furthest point to try and locate the fault but each socket is showing 1 leg of ring to be ok & 1 leg to fail IR test. This would suggest to me they are all on radials from a single point then spuring off to downstairs from each socket or there are multiple failures?
- I tried to trace the cables using a circuit finder but the device kept strobing to show live (or as i believe to show it's looping). I did a continuity test between ring live and main earth with everything disconnected (TNS) and got a reading of 1.4Kohms. If there is any continuity between live and earth on a tns does this mean the ring is touching the water pipes and going outside for a walk?
- I managed to have a look under the bathroom floor to find one leg which seemed ok at that point. Other sources of water I'm thinking of are radiators, boiler (out of use) and pet urine.