Hi All,

Will post an introduction on the new members forum but need to blurt out my question while its still in my head.

Me and Mrs JimmyB1988 have moved into our first house, it has a split consumer unit, half on RCD half not, my sockets were on the half without an RCD. One breaker does all the sockets including the Kitchen. So I moved the sockets breaker over to the RCD side, moved the neutrals too over to the RCD neutral bar. But it keeps tripping the RCD, all works fine on non protected side, i insulation resistance tested the circuit and reads 0Mohms between line + neutral, neutral + earth, line + earth? Confused?
[ElectriciansForums.net] Ring Main Tripping RCD, Line to Earth reads 0


Can anyone think of anything obvious?

Thanks Guys/Girls
[ElectriciansForums.net] Ring Main Tripping RCD, Line to Earth reads 0
 
Hi,
Firstly I see your qualifications are in Engineering, although you may have electrical experience.
You need to double check the cables you have moved across are definitely the Line Neutral & EARTH for that circuit.
Secondly , unplug everything from the Ring Main to check whether it may be an appliance fault.
Finally, If you are using an IR tester it may show a dead short, but can be higher due to the resolution of the meter.

This should get you started anyway.

Regards.
 
Hi,

Line - Neutral 0.00 Mohms
Line - Earth 0.00 Mohms
Neutral - Earth 0.00 Mohms

I have unplugged everything in every room, and the boiler is on a spur from the ring which i've knocked off. Cooker is on the ring, but i knocked that off too. (As I type I realize the extractor is on the ring too so i will try again with that disconnected)

I switched off the main switch at the c/u, I disconnected the ends of the ring from the breaker and neutral and earth bar.

R1+R2 is 0.32 ohms
 
When you did the IR test what test voltage did you have your tester set to? If there's still something connected such as an electronic ballast or TV amplifier if might give you low IR readings due the test voltage exceeding the clamping voltage of the built-in surge arrestors.
 

Reply to Ring Main Tripping RCD, Line to Earth reads 0 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
857
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top