Another thought, if some thing bad were to happen, and the circuit is of a design that isn’t in BS7671, the installer wouldn’t or have a leg to stand on. If something bad were to happen and the circuit was designed along the guidelines of BS7671 then the installer would be totally in the clear.
If people are installing circuits, that have already been described as not being discussed in BS 7671, are we not complying with the E@WA?
We are indeed talking about a circuit serving sockets in this thread and not lighting or circuits serving appliances so I’m not sure why you brought these scenarios in to it? As you said,We all install circuits regularly which are of a design that isn't in BS7671.
There is no lighting circuit in BS7671.
There is no dedicated circuit for an appliance in BS7671.
There is no 3 phase circuit in BS7671.
There is no distribution circuit in BS7671.
Etc
Etc
There are rules and regulations to allow the safe and compliant design of any circuit, that part of the point of the regulations existing.
There are only standard circuits in BS7671 for final circuits supplying multiple socket outlets.
[automerge]1592680805[/automerge]
The only circuits that are specifically 'discussed' in BS7671 are final circuits supplying sockets.
If we stuck to only ever installing circuits which are 'discussed' in BS7671 we would not be able to install a lighting circuit, cooker supply, any 3 phase circuit etc etc!
Great stuff marky the sparky. So, short answers please:[a ring final circuit should be continuous rings (as evidenced by the testing we are required to carry out). So, assuming in this situation the CPC is continuous, it's compliant.
"543.7.2 Socket-outlet final circuits
543.7.2.201 For a final circuit with a number of socket-outlets or connection units intended to supply two or more items of equipment, where it is known or reasonably to be expected that the total protective conductor current in normal service will exceed 10 mA, the circuit shall be provided with a high integrity protective conductor connection complying with the requirements of Regulation 543.7.1. The following arrangements of the final circuit are acceptable:
(i) A ring final circuit with a ring protective conductor. Spurs, if provided, require high integrity protective conductor connections complying with the requirements of Regulation 543.7.1
(ii) A radial final circuit with a single protective conductor:
(a) the protective conductor being connected as a ring, or
(b) a separate protective conductor being provided at the final socket-outlet by connection to the metal conduit or ducting, or
(c) where two or more similar radial circuits supply socket-outlets in adjacent areas and are fed from the same distribution board, have identical means of short-circuit and overcurrent protection and circuit protective conductors of the same cross-sectional area, then a second protective conductor may be provided at the final socket-outlet on one circuit by connection to the protective conductor of the adjacent circuit
(iii) Other circuits complying with the requirements of Regulation 543.7.1."
Since this is about the implementation of high integrity earthing, we once again have to make an assumption. In a domestic situation it's unlikely high integrity earthing will have been installed.
"643.2 Continuity of conductors
643.2.1 The continuity of conductors and connections to exposed-conductive-parts and extraneousconductive-parts, if any, shall be verified by a measurement of resistance on:
(i) protective conductors, including protective bonding conductors, and
(ii) in the case of ring final circuits, live conductors."
Testing... we are required to conduct specific tests on ring final circuits. These can easily be done but the results sheets are not designed to record multiple ring result sets for a single 'circuit'. I would perhaps use two lines of the schedule of results to ensure I captured all the relevant information, with clear labelling applied to the circuits within the consumer unit to allow easy identification later (and thus allow easy cross referencing of results).
So, now lets look at some possible areas this installation could breach the regulations.
@Pete999 has already provided one in the form of 134.1.1. This is however somewhat subjective. If we assume the cable is sized correctly, it's properly supported along it's run, it's properly installed (protected against mechanical damage for example, all conductors are properly identified etc.) and the connected accessories are compliant with the required standards, the only possible reason we may be in breach is if the manufacturers instructions provide guidance on the number of conductors in a particular termination at the consumer unit. With a 3036 rewireable board this could be a problem, with early MCBs it could be a problem, with 60898 compliant MCBs it's not likely to be an issue (4 x 2.5mm sq. conductors) but with 61009 compliant RCBOs it may be a problem due to the reduced size of the terminals. So, an assessment of the overall installation and the terminations should be made to determine if there are any issues (this is no different to any other circuit).
"314 DIVISION OF INSTALLATION
314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid danger and minimize inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Chapter 46 and Section 537)
(iii) take account of hazards that may arise from the failure of a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor (PE) currents not due to a fault
(v) mitigate the effects of electromagnetic disturbances (see also Chapter 44)
(vi) prevent the indirect energizing of a circuit intended to be isolated.
314.2 Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device.
314.3 The number of final circuits required, and the number of points supplied by any final circuit, shall be such as to facilitate compliance with the requirements of Chapter 43 for overcurrent protection, Chapter 46 and Section 537 forisolation and switching and Chapter 52 as regards current-carrying capacities of conductors.
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board. The wiring of each final circuit shall be electrically separate from that of every other final circuit, so as to prevent the indirect energizing of a final circuit intended to be isolated."
This is the section I think we are most likely to be in breach of when considering this arrangement.
314.1 (i) as this arrangement has the potential to take out all the sockets in the event of a fault, (ii) arguably this is a case of inconvenience for the installation user whilst we are working because whilst we can facilitate safe inspection, testing and maintenance, we have to shut off all sockets which may result in incovenience for the user, (iv) nuisance RCD tripping could be a problem, but no more than two ring circuits connected to different breakers on the same RCD (a situation that occurs quite frequently with split load boards).
314.2 ordinarily this may not be a problem, sure it's inconvenient but what happens if say someone has a new requirement for some medical equipment? Having all the sockets on a single circuit wouldn't be a good plan in this case as a fault could take out the supply to life support equipment. Arguably this should be considered and addressed when the equipment is installed, but it may not be and thus we could have a dangerous situation.
314.4 this point has resulted in a lengthy discussion in the past in relation to a similar topic (is it ok to combine radial circuits on one MCB). It could be argued that each ring is a final circuit in it's own right and thus should be supplied by a separate way but as the definition of circuit is somewhat wishy washy, it can be argued that 'a circuit' is defined as whatever is connected to a particular way in the distribution board.
"411 Protective Measure: Automatic Disconnection of Supply"
If both rings are installed correctly and are capable individually of meeting the requirements for this, when connected to the same protective device they should continue to meet these requirements. We would of course need to check the earth fault loop impedance and as good practice check the line-neutral loop impedance to ensure it doesn't exceed the maximum EFLI for the circuit breaker (to ensure we can meet our disconnection time for LN faults). Clearly we need to conduct more testing, but essentially this is no different to any other circuit.
These are my thoughts about it. I don't believe there are any clear contraventions of the regulations with such an arrangement. Much of it is down to one's interpretation/views. From a safety perspective, assuming the circuit is permitting no option; not to be disregarded or modifiedconnected to it's own MCB.
Discuss
We are indeed talking about a circuit serving sockets in this thread and not lighting or circuits serving appliances so I’m not sure why you brought these scenarios in to it?
Why wouldn’t you?Would I install like this? No.
I’m sorry, I didn’t write that! That was a post from SC. I accidentally quoted it and spent the next 20mins and two bottles of beer trying to delete it in the edit option!Great stuff marky the sparky. So, short answers please:
What is the danger?
What reg(s) does it break?
Sure thing fella. I'm still interested in your answers though.Why wouldn’t you?
[automerge]1592682785[/automerge]
I’m sorry, I didn’t write that! That was a post from SC. I accidentally quoted it and spent the next 20mins and two bottles of beer trying to delete it in the edit option!
I don’t see any real danger having taken into account loads on both circuits.Sure thing fella. I'm still interested in your answers though.
I don’t see any real danger having taken into account loads on both circuits.
As for the regs that it contravenes, it would depend on how you interpret the regs. I have had this arguement with SC and others before now and it all came down to how we interpreted the regs. Most of the her post makes sense but I disagree in what I think the spirit of what the regs mean about the definition of a circuit. I have brought this up with NICEIC tech, NICEIC assessor, IET, and a well known You Tuber and all have the same opinion as I do. It comes down to making the installation simple. Bunching circuits together in OCPD complicates so it goes against what the regs are trying to achieve. This is why BS7671 is constantly being updated, not just because of the advent of new tech but to take grey areas away. I’m not big headed enough to claim that I’m correct as the way the regs are written about the definition of a circuit leaves a lot still in the grey area but until they re write it we will be having this argument at Ad infinitum.
Fun though isn’t it!
Why wouldn’t you?
I have had this arguement with SC and others before now and it all came down to how we interpreted the regs. Most of the her post makes sense but I disagree in what I think the spirit of what the regs mean about the definition of a circuit. I have brought this up with NICEIC tech, NICEIC assessor, IET, and a well known You Tuber and all have the same opinion as I do. It comes down to making the installation simple. Bunching circuits together in OCPD complicates so it goes against what the regs are trying to achieve. This is why BS7671 is constantly being updated, not just because of the advent of new tech but to take grey areas away. I’m not big headed enough to claim that I’m correct as the way the regs are written about the definition of a circuit leaves a lot still in the grey area but until they re write it we will be having this argument at Ad infinitum.
Fun though isn’t it!
But to pin it down a bit more, davesparks said earlier that the only circuits that are specifically ‘discussed’ in BS7671 are those supplying multiple sockets outlets. These are in appendix 15 and as they are in BS7671 they are a ‘requirement’. Please see my previous post about the definition of ‘requirement’. Requirements are not to be adjusted, tinkered with, or adapted.
Do not be offended if I ammend that a bit but a circuit is defined by the Overcurrent Protective Device (Fuse/MCB) therefore several radials (or rings) connected at one fuseway is one circuit. Whether it`s bow tie or trees or whatever it`s just one circuit.Although radials and not ring finals you are allowed to put multiple 'circuits' in one MCB in some foreign regs, France, Norway and Germany being amongst them i believe. I don't think it's inherently unsafe just because it's against the regs, just poor practice when done in the UK.
I don't know if the regs have changed since i was last there (in like 2011) but i'm fairly sure you could have more than one radial 'circuit' going into a disjoncteur in France. I remember seeing a picture taken from a book showing three separate lighting radials going into the same MCB and no mention of a limit. Obv they wouldn't do real circuits there because they don't use them, it's all radial.Just to make it clear in France, Germany and Norway it is against the Regulations to have more than one circuit to a MCB, if we are talking Radials, 12 sockets to a 2.5mm circuit and 8 to a 1.5mm circuit, there are quite a few specific appliances that have to be on their own circuit.