Question I have is, is it ok to have x2 ring main circuits on one 32amp type B MCB??

If so does this meet the current regs.

TIA.
 
Soi disant,
Nice diagrams and well put.
Yes I like it.

Ok the point I was making.

With a bridge that makes a ring final become a "fig 8" it means that we tend to lose control of which leg gets more of the current x usage factor. A I said we don`t usually go to great lengths do control this however we do a quick approx to see if it looks badly slanted in favour of one leg or the other and then perhaps re-adjust our plan in order to balance it up a bit. This helps with heating issues and therefore aging of cables and helps reduce overloads of cables.

I`m not suggesting that fig 8 or indeed that lovely matrix thingy you drew for use is going to cause fires and threaten life everytime it`s used, far from it.

It is complicated enough to make predictions even with a well designed ring final and the fig 8/matrix complicates this further.
In reality, much of the time, no great problems should arise from it and if every ring final was done that way I don`t think we`d find streets littered with dead bodies.

However, of all the differing combinations of power drawn at various points around the ring then this arrangement is far more difficult to follow, calculate and therefore enjoy the most reasonable aspects of ring benefits as originally conceived for current flow considerations. It also makes it difficut to test properly too (OK that one can be said, to a degree, about the 2, 3, 4, umpteen rings on one ring final circuit too!)
 
It's testing which is the problem, I think. Without the predictability/consistency of readings from a proper, single, ring it's harder to spot problems such as multiple socket spurs.

But as for loading and balance - I won't mind if I prove myself wrong with some worked examples, (or if someone else does to save me the effort ?), but my initial feeling is that any cross-connections which make a figure of 8 or anything else just add current paths and thus lower the current flowing in them, not increase it.

I can sort of envisage a scenario where a section near the origin of the ring could become unbalanced, but I'm not sure how improbable it is. Need to do some sketches.

Anyone out there with circuit design software which could be used to analyse different scenarios?
 
It's testing which is the problem, I think. Without the predictability/consistency of readings from a proper, single, ring it's harder to spot problems such as multiple socket spurs.

But as for loading and balance - I won't mind if I prove myself wrong with some worked examples, (or if someone else does to save me the effort ?), but my initial feeling is that any cross-connections which make a figure of 8 or anything else just add current paths and thus lower the current flowing in them, not increase it.

I can sort of envisage a scenario where a section near the origin of the ring could become unbalanced, but I'm not sure how improbable it is. Need to do some sketches.

Anyone out there with circuit design software which could be used to analyse different scenarios?
Not really other than it's not called a ring main a ring main is a distribution circuit it's ring final circuit if you get your terms correct you may get some better responses
 
If I start with this:

View attachment 84116

and add a loop like this:

View attachment 84117

or if I start with this:

View attachment 84118

and add a link across the middle to end up with the same figure of 8, which cable(s) become at risk of being overloaded that would not if I'd done this:

View attachment 84122

?


The more paths there are for current to flow to each point of loading the less flows in any given one, not more.

Ignoring the practical realities of actually wiring it, a "full mesh" topology of interconnections

View attachment 84124

would minimise the current flowing in every single cable (apart, obv, from the ones from the OPD to the "first" and "last" sockets, but those cables are never affected by any interconnection topology anyway).

And the more connections you have the harder it becomes to turn the circuit into radials, or to create multi-socket branches, by cutting connections.
youneed to get out more. don't the pubs open soon?
 
Not really other than it's not called a ring main a ring main is a distribution circuit it's ring final circuit if you get your terms correct you may get some better responses

Pete, I think you might have quoted the wrong person.
 
If you are referring to me Tel, then nothing gets up my snout more than Wannbee's quoting something they know little or nothing about post ban waiting, still no one likes the truth these days do they?
i was referring to the poster who drew all those figure 8 etc. circuits.
 
Pete, I think you might have quoted the wrong person.

probably did in my state of mind
It happens. A few times (not here) in the past I've had "discussions and debates" (ahem...) lasting multiple posts where I've misattributed what had been said. The arguments over what had been said were valid, but with the wrong person.

Worse things happen at sea.
 
Actually, just to be a bit naughty - what is unsafe about a large number of radials, each one having not more than one twin socket and all connected by say one 32A MCB. Not actually unsafe proving the joints are reliable both electrically and mechanically and all volt drop and Zs are catered for.
I wouldn`t like to see it but it would not cause piles of dead bodies to litter the place.
Bring back (and uprate) the octopus....
 

Reply to Ring main. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Well we called it a room, but it was only a hole in the ground covered with bit of canvas.
Replies
13
Views
424
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
396
  • Question
Thanks for all your input guys. It seems to be that it’s down to personal preference on the best thing to do/if it’s appropriate. In my head I...
Replies
18
Views
2K
  • Question
As long as you can carry out all the necessary testing, certification, are insured to do the work and all is carried out to Amendment 2 of the regs
Replies
1
Views
562
  • Question
Suggests yes, but doesn't prove it, not all imperial cables were tinned.
Replies
15
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks