Ring spurred at origin? | on ElectriciansForums
Discuss Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net
Manchester
Hi all,
DIYer here. My garage has a double socket fed by 4mm2 twin and earth connected to the same circuit breaker has the ring main for the sockets upstairs in the house. The MCB is a B32.
Is the feed in the garage considered a spur from the ring main or is it a separate radial circuit which happens to be on the same MCB? Ideally I'd like to add more sockets to the circuit in the garage (using 4mm2) but is this safe or allowed?
Thanks.
It would be considered a spur and being 4.0 its method of installation would dictate whether it could carry 32A and be added to. Spurred points from ring final circuits are normally limited as to the number of points which can be served but the 4.0 clouds that a bit. It sounds like the garage socket has been a later addition and connected to the existing ring final circuit and if the existing circuit is wired using 2.5/2.5 conductors it is not ideal to have differing sizes at the same protective device, are there spare ways in your consumer unit.
If the 4mm2 is on the same circuit breaker as the RFC then it is a Spur, as for adding more sockets to the 4mm2you would need to swap the double socket for a Fused spur unit and add sockets from that spur unit, remember the extra sockets will be limited to 13Amps governed by the fuse in the spur unit.
Another method would be to take the 4mm2 to a seperate CB (providing there is one) and form a 32 Amp Radial to your Garage (assuming it's an atatched Garage), the proviso being is that your Garage would need RCD protection, if the garage is a standalone then a different set of rules apply.
The question as to whether this 4.0 can take 32A is down to its installation method. The spur is somewhat unconventional as it stands.
The 4.0 is clipped along a roof joist in the garage, exposed to the air, no insulation etc. The consumer unit is actually in the garage, but there is no space for additional circuits.
We've only been in the house a few months so trying to understand what work has been done previously.
Theoretically you could add to it but the best course is to connect to its own protective device but this is obviously not possible.
The spur is 4.0 clipped direct so in theory if he uses the same size of cable and installation method as the existing he could add direct to it. Personally I would like to see it on its own circuit.
A spur equates to One double or single socket
A One fused or unfused spur unit
A One fusedspur feeding a Fixed appliance.
The only way you can add more than one socket is on a 4mm2 32 or 30 Amp radial circuit if adding more than one the the cable used must be the same as the circuit is wired in 4mm2, this is the same for a 20Radial circuit wired in 2.5mm2
As the circuit in question is a Ring FC adding more than one unfused socket is not allowed
Reply to Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net
Haha yes, it is. Must be a northern expression. Have a Google 😂
Thanks for the advice.