That would be valid so long as the OCPD is suitable for the use.Although, when you think about it, with 2 rings and 1 radial on a single device it only only takes 2 snips and a bit of trimming and you have 5 radials on a single protection device.
So with 32A and 2.5mm it should be a RFC only, but with 4mm it could be a radial on 32A (in many cases, but subject to method for CCC)
If you have a dubious mix of radials and spurs that are not OK then simplest safe option is to drop OCPD to 20A as then it protects the 2.5mm however used.
Sometimes you would see RFC on 20A fuse wire if the supply Ze was too high tor meeting 0.4s disconnection, etc. While not as useful in terms of diversity as 32A (i.e. number of mixed loads up to 13A supported) it works just fine if that limit is respected.