martom

Hi, another question which I hope you can help me ;)
I'm doing kitchen rewiring. The old ring was running on 3x 4mm cable.
Is it OK by the regulations to use part of the old ring (from CU to kitchen, and from kitchen to CU) and fit in in between 2x4mm 1.5mm earth size.

In my opinion this should be absolutely fine, I will just get better cpc reading on test, but maybe I am wrong?
Thanks
Tom
 
You could always get an electrician in, as this will be covered under part p. no point messing around, let a professional do it.
I know its under part P, my qualifications has been recognised in UK, I am even Part P registered, just in country where I did my apprenticeship and qualifications we haven’t used rings...
 
I mean the cable which is fitted already is twin and earth, but earth is 4mm exactly like L and N.
The circuit is a ring, I want to cut out the old kitchen part of the ring and partly rewire using T&E 4mm, 1.5mm earth. The live wires will stay the same size - The earth will be partly 4mm, partly 1.5mm.....
 
Last edited by a moderator:
I don't think it would be a problem, can you not replace the whole ring rather than messing around with existing cables, you would need to make sure your jb (if using them) are accessible. Is it wired in singles, swing as the earth is the same as the live and neutral. Also are you sure it's 4mm and not the old imperial stuff?
 
I don't think it would be a problem, can you not replace the whole ring rather than messing around with existing cables, you would need to make sure your jb (if using them) are accessible. Is it wired in singles, swing as the earth is the same as the live and neutral. Also are you sure it's 4mm and not the old imperial stuff?
This is something I need to check- as the colours are prior 1977 :(

- - - Updated - - -

3 cores in cable
 
Then what you have there is not T+E but .......well who knows what you have

There is nothing wrong with using the feed and return legs of a ring in 4mm and then wiring the inside legs in 2.5mm/1.5mm or as you said 4mm/1.5mm.

You will just need to ensure that the existing cable is in good condition, and that your VD. R1+R2 etc are within tolerances
 
Sounds like conduit and singles to me, thus fairly difficult to extend the rfc. As said above I would probably re-wire the lot if its easy enough.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Ring wires question
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
martom,
Last reply from
shay.sparky,
Replies
21
Views
2,232

Advert

Back
Top