Yes it complies with the regs. Changed a fuse box and have to do an EIC so on the schedule of test results I was just wondering how to record an existing spur off a ring circuit.
 
Yes it complies with the regs. Changed a fuse box and have to do an EIC so on the schedule of test results I was just wondering how to record an existing spur off a ring circuit.

Hawk, not really sure what you are trying to record. you are bound to get odd Zs results when spurs are involved, as long as the ZS is within the max permissible I shouldn't worry
 
Whilst testing Zs on the ring you get, say, 0.47Ω on each socket on the ring and readings of, say, 0.54Ω, 0.63Ω and 0.59Ω on the, say, three spurs then you would record the Zs of the ring as 0.63Ω, as this is the highest value. Your limit on a B32 is 1.1Ω at ambient so the circuit is fine.
The circuit details are just that details of the entire circuit, not parts of it.
 
Ok. I have seen on other forums where people have said that say for instance a fused spur is taken off a ring for a lighting circuit. Then they would record the lighting circuit as a seperate circuit with 5amp 1361 as the fuse. Even though it is spurred off a ring.
 
Ok. I have seen on other forums where people have said that say for instance a fused spur is taken off a ring for a lighting circuit. Then they would record the lighting circuit as a seperate circuit with 5amp 1361 as the fuse. Even though it is spurred off a ring.

Your original post didn't mention a fused spur, I think all the replies you have had are under the assumption that the spur you originally asked about was a 13amp socket outlet spurred from the ring final circuit, confusion reigns
 
To start with, I would mention the situation in the 'comments on the existing installation' section of the report.

The spur should be unswitched, with a 5A fuse also labeled for 5A fuse max. The as for the lighting circuit should then fall within the allowed As for fuse in spur.
 

Reply to ring with spurs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Very technical :D
    • Like
Replies
9
Views
448
  • Question
Thanks for the advice.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top