Hi all, after some advise please.

I work as a maintenance engineer at a school and recently we had an outside contractor come in and fit an external Rolec EV unit to the outside of our workshop under the grant scheme.

I don't know much about the installation of these units but I did do part P several years ago so I have some electrical understanding. Consequently I do have some concerns about the installation which may be an issue or maybe more likely just my lack of knowledge!

The EV unit has the internal RCD for the AC supply, and the seperate RCD module for any DC injected back into the circuit. It has been installed with an internal isolator, meter and comms box which all seems fine.

However,

1) The contractors installed a new circuit in our DB for the EV supply but there is no test certificate to show results.

2) The unit is installed in our yard where we store gas cylinders and fuel. The charging unit has been installed directly above a metal storage unit that contains gerry cans of petrol. Gas cylinders are housed in a cage about 2 meters away.

3) The earth from the EV unit has been connected to the building's steel rainwater downpipe which goes under the ground but I've no idea how deep the pipe goes.

Are these issues cause for concern?

I'd appreciate your thoughts.

Many thanks.
 

Attachments

  • [ElectriciansForums.net] Rolec EV installation
    20191129_125054.jpg
    181.6 KB · Views: 68
  • [ElectriciansForums.net] Rolec EV installation
    20191129_125056.jpg
    216.4 KB · Views: 67
I do this all day every day and I wouldn't say anything about it - if I saw this during an inspection I'd just assume it was a bond to the electrical earth as would my colleagues
That could well be a natural assumption, do you never verify this. Would this not be deemed an important part of the inspection??
 
Last edited:
Do you have a 12 monthly test of the LPS.

Our LPS is required to be tested on an 11 monthly cycle to keep track of any season variations.
Ive never known if this is normal or a peculiarity of our storage license.
[automerge]1575067988[/automerge]
I do this all day every day and I wouldn't say anything about it - if I saw this during an inspection I'd just assume it was a bond to the electrical earth as would my colleagues

But it appears to be undersized for the size of the installation and its above ground when it should be below ground level at an earth rod termination.
 
That could well be a natural assumption, do you never verify this.
We don't have enough time really, some days I have 5+ inspections to do and if something isn't going to affect the LPS I can't justify investigating further

My view is that it's down to the electrician who made the connection to determine whether it's safe or not
 
We don't have enough time really, some days I have 5+ inspections to do and if something isn't going to affect the LPS I can't justify investigating further

My view is that it's down to the electrician who made the connection to determine whether it's safe or not

How can you thoroughly inspect 5 sites in a day?
How do you know if it isn't going to affect the LPS if you don't investigate?
 
We don't have enough time really, some days I have 5+ inspections to do and if something isn't going to affect the LPS I can't justify investigating further

My view is that it's down to the electrician who made the connection to determine whether it's safe or not
I find that an odd reply as few electricians are conversant with the Regulations you are testing to. I would suggest time factors are not relevant. So knowing the relevant requirements is this an acceptable situation.
 
Our LPS is required to be tested on an 11 monthly cycle to keep track of any season variations.
Ive never known if this is normal or a peculiarity of our storage license.
[automerge]1575067988[/automerge]


But it appears to be undersized for the size of the installation and its above ground when it should be below ground level at an earth rod termination.
11 monthly is correct to BSEN 62305 to account for seasonal changes in ground conditions as you say.

I don't know if it's undersized because it's for the earthing of the EV charger nothing to do with the LPS but we would connect an EQ bond wherever possible you can't always get it underground.
[automerge]1575069932[/automerge]
How can you thoroughly inspect 5 sites in a day?
How do you know if it isn't going to affect the LPS if you don't investigate?
You just develop the speed over the years. Lightning Protection can be complex on things like refineries which can take weeks to inspect but general systems for example a block of flats with 15 downconductors it would take 30-40 minutes to inspect the air termination network and maybe another 30-40 minutes to test the earth rods. With the recent obsession with compliance testing we are flooded with work and you wouldn't last if you couldn't keep up.

I don't know how to answer your other question, not much shy of vandalism will stop LP from working if it's maintained.
[automerge]1575070401[/automerge]
I find that an odd reply as few electricians are conversant with the Regulations you are testing to. I would suggest time factors are not relevant. So knowing the relevant requirements is this an acceptable situation.
I don't know if it is acceptable or not. I wouldn't bat an eyelid if I saw this on a job but that being said, it is not really appropriate to connect it where it is as it's likely to get disturbed which I guess could cause the EV charger to not be earthed?
 
Last edited:
Hmmm, interesting. We have a lightning system. In the 15 months I’ve been there, never seen it tested. Are all LPS the same, or is the testing only required for petrochemical establishments for example?
 

Reply to Rolec EV installation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
The last couple of de-loops that I have been involved with had the single phase supply replaced with a three phase cutout (as I believe the DNOs...
Replies
5
Views
1K
  • Question
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help. I installed an EV...
Replies
0
Views
205

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top