Ah ok , was going to fit it high up , but I assume it's switch level then . My bad thinking of small garage roller doors , see told you I was domestic ,lol
 
You need to ask the installer as I said many of these are now at high level by the shutter mechanism. If it is high level I would not be fitting an rcd at the socket position.
 
high level commando socket dedicated to the door. no RCD required. maybe a RA to cover your arse.
 
is the door going to be 1 phase or 3 phase. ? the 3 phase ones I'vecome across need a 5 pin socket.so a 5 core SWA as well.
 
Why do they need a plug & socket?

If it is simply for a means of isolation for maintenance then a lockable rotary isolator next to their box would do and then no RCD needed.
 
Why do they need a plug & socket?

If it is simply for a means of isolation for maintenance then a lockable rotary isolator next to their box would do and then no RCD needed.
A lot of the recent new doors I've seen come with commando plug already fitted, it's like they're expecting them to fail and it's easier, and cheaper, to send cheap labour just to swap it over rather than a spark to mess with silly things like wiring...

Seen one which was fed from a 16 amp commando which was plugged into a standard BS1363 socket outlet... ?
 
it's like they're expecting them to fail and it's easier, and cheaper, to send cheap labour just to swap it over rather than a spark to mess with silly things like wiring...
Ah, follow the money and you see the reason :(

Externlising the cost as they say, making your installation more expensive to overcome their crap quality.
 

Reply to Roller Door Feed 3 phase (RCD?) in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top