Running Cable to Garage | on ElectriciansForums

Discuss Running Cable to Garage in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 25, 2019
Messages
18
Reaction score
9
Location
Alberta
We are going to run Teck90 or ACWU cable underground from house to garage. There will be just a 60A breaker in the house and garage for now but want to lay a large enough cable to carry 100A in the future. We have approximately 60 ft of ACWU #3/0 aluminum to make the run. It is about 2" in diameter, the 3/0 conductors are close to 1/2" so it's over sized which will make it a little more work to install.
Some answers to my questions might make it easier.
- With the cable being just under 2" diameter what diameter does the PVC conduit have to be up to the LB fitting? Is 2 1/2" good enough? 4" seems like overkill.
- We need to run the 3/0 into a transition box, then come out of the box with #3AWG because the 3/0 won't fit the panel.
If I can't tame this configuration down a bit, maybe we'll just buy some ACWU with #3AWG copper.
 
This is a UK based forum, so I’m afraid your terminology is getting lost in translation.

Have to admit, the OP has posted in the correct section of the forum.
I forgot we had a 'Non UK Electrical Works' section.
 
Have to admit, the OP has posted in the correct section of the forum.
I forgot we had a 'Non UK Electrical Works' section.
I moved it this morning, going to try and keep all these that keep popping up in here.
 
I guess it's too late for me to edit my original post. It is not UK in nature, and was poorly written with incorrect terminology so I will revise it here:

We are thinking of running ACWU 3/0 AWG from house to garage (because it is free material). The #3/0 AWG is too big to work with in the panel so we would have to use a transition box. Can the LB be used for that?

Is using this free oversized material going to be more headache than it is worth? The CEC conductor ampacity chart says #1 AWG aluminum is good for 100A.

I will explain the acronyms in my next post. Thanks.
 
ACWU (not Ammalgamated Clothing Workers Union:) cable is for exposed and concealed wiring in dry or wet locations where exposed to the weather, and hazardous places. It has aluminum conductors, and a spiral flexible armor but no inner sheath around the conductor bundle.

TECK cable is of Canadian origin but used in many places around the world now. It has similar application but has copper conductors, an inner sheath, and a spiral flexible armor. 2 or 3 times more expensive than ACWU.

AWG: American Wire Gauge
LB: Stands for line box. It is often used at the point where you will begin pulling wire through the conduit.
CEC: Canadian Electrical Code

Have a good day UK.
 
Sometimes free is just too expensive, for such a short run just use the proper sized conductors, it will be a better and cleaner install. BTW, trying to splice 3/0 in a LB would be like trying to stuff 10 pounds of manure in a 5 pound bag, not sure about the CEC, but the NEC would not allow it, there is insufficient volume to do so.
 
Sometimes free is just too expensive, for such a short run just use the proper sized conductors, it will be a better and cleaner install. BTW, trying to splice 3/0 in a LB would be like trying to stuff 10 pounds of manure in a 5 pound bag, not sure about the CEC, but the NEC would not allow it, there is insufficient volume to do so.
LOL! I like that one, I'm going to use it. 10lbs into 5lb bag:)
I was going to use a six inch box instead of an LB. I would be transitioning to 1 AWG in the box using 1/2 split bolts. I would rather use the 1AWG for sure but I'm going to do the arithmatic because the TECK fittings etc. are more expensive and it might neutralize any savings anyway. Thanks
 
I guess it's too late for me to edit my original post. It is not UK in nature, and was poorly written with incorrect terminology so I will revise it here:

We are thinking of running ACWU 3/0 AWG from house to garage (because it is free material). The #3/0 AWG is too big to work with in the panel so we would have to use a transition box. Can the LB be used for that?

Is using this free oversized material going to be more headache than it is worth? The CEC conductor ampacity chart says #1 AWG aluminum is good for 100A.

I will explain the acronyms in my next post. Thanks.
Could have fooled me, I wouldn't have picked up on poor terminology as I am clueless about american/Canadian electrical practices
 

Reply to Running Cable to Garage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

Replies
5
Views
188
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
730
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

And if it's a garage then use metal clad accessories.
Replies
5
Views
453
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
259

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top